[Equest-users] Tip for unmet heating hours in VAV systems
    Maria Karpman 
    maria.karpman at karpmanconsulting.net
       
    Fri Sep 16 12:59:44 PDT 2011
    
    
  
Pasha and Bill,
 
I also often use this keyword, but usually increase the fraction
incrementally by 0.1 instead of just setting it to 1, to avoid
out-of-control behavior described in DOE2 help. Here is the related quote:  
Some reverse-acting VAV systems may go out of control if the maximum heating
airflow is not restricted . As the zone temperature drops, the box
progressively opens to deliver more air. However, since the supply air is
usually lower than the zone temperature, more coil energy is required to
offset the non-useful reheat (difference between zone temperature and supply
air temperature), potentially leaving less coil/boiler capacity available
for useful heating. As a result, a terminal at full flow may deliver less
useful heating than at lower flow, resulting in an out-of-control situation;
the box may go to full flow even though a reduced flow would heat more
effectively. The solution is to restrict the maximum flow during reheatng
coil and/or boiler is not sized sufficiently large, 
I did see this scenario happen in some projects, when adjusting the value of
the keyword up beyond certain point increased heating, cooling, and fan
power, but did not help much with under-heating.  
Thanks,
Maria 
 
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Pasha
Korber-Gonzalez
Sent: Friday, September 16, 2011 3:23 PM
To: Bishop, Bill
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Tip for unmet heating hours in VAV systems
 
Thanks Bill--I think this will be helpful.  I currently have a baseline
model with whacked underheated hours and with upsizing ratios and autosized
calcs nothing is changing for me.  I will try this input adjustment and see
if it works.
 
Thanks for sharing!
Pasha
On Fri, Sep 16, 2011 at 8:33 AM, Bishop, Bill <wbishop at pathfinder-ea.com>
wrote:
Thought I'd share a tip for addressing unmet heating hours in VAV systems
using eQUEST 3.64.
 
eQUEST 3.64 adds the HMAX-FLOW-RATIO keyword in System -> Fans -> Flow
Parameters. The default value is the greater of the fan MIN-FLOW-RATIO and
0.5, but this value is determined by the program and you don't see it when
you look at the Flow Parameters tab. Entering a value of 1.0 corrected an
unmet heating hours problem for me that appeared when I opened a model in
3.64 that I originally created in 3.63. This works for both VAVS and PVAVS
system types.
 
Regards,
Bill
 
Senior Energy Engineer
 
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send  a blank message to
EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
 
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110916/0a1da5b7/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 22378 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110916/0a1da5b7/attachment.jpeg>
    
    
More information about the Equest-users
mailing list