<div>Thanks Bill--I think this will be helpful.  I currently have a baseline model with whacked underheated hours and with upsizing ratios and autosized calcs nothing is changing for me.  I will try this input adjustment and see if it works.</div>
<div> </div>
<div>Thanks for sharing!</div>
<div>Pasha<br><br></div>
<div class="gmail_quote">On Fri, Sep 16, 2011 at 8:33 AM, Bishop, Bill <span dir="ltr"><<a href="mailto:wbishop@pathfinder-ea.com">wbishop@pathfinder-ea.com</a>></span> wrote:<br>
<blockquote style="BORDER-LEFT: #ccc 1px solid; MARGIN: 0px 0px 0px 0.8ex; PADDING-LEFT: 1ex" class="gmail_quote">
<div lang="EN-US" vlink="purple" link="blue">
<div>
<p class="MsoNormal">Thought I’d share a tip for addressing unmet heating hours in VAV systems using eQUEST 3.64.<u></u><u></u></p>
<p class="MsoNormal"><u></u> <u></u></p>
<p class="MsoNormal">eQUEST 3.64 adds the HMAX-FLOW-RATIO keyword in System -> Fans -> Flow Parameters. The default value is the greater of the fan MIN-FLOW-RATIO and 0.5, but this value is determined by the program and you don’t see it when you look at the Flow Parameters tab. Entering a value of 1.0 corrected an unmet heating hours problem for me that appeared when I opened a model in 3.64 that I originally created in 3.63. This works for both VAVS and PVAVS system types.<u></u><u></u></p>
<p class="MsoNormal"><u></u> <u></u></p>
<p class="MsoNormal">Regards,<u></u><u></u></p>
<p class="MsoNormal">Bill<u></u><u></u></p>
<p class="MsoNormal"><u></u> <u></u></p>
<p class="MsoNormal"><img alt="Senior Energy Engineer" src="cid:image001.jpg@01CC7459.C3C43970" width="486" height="116"><u></u><u></u></p>
<p class="MsoNormal"><u></u> <u></u></p></div></div><br>_______________________________________________<br>Equest-users mailing list<br><a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>