Dear e-Quest users,

We have received a review comment for one of our projects stating: From the
simulation report provided (SV-A System Design Parameters report), it does
not appear that the Baseline fans in parallel VAV fan-powered boxes are
sized for 50% of peak primary airflow and modeled with 0.35 W/cfm (0.74
W/L/s) fan power and a minimum flow setpoint of 30% of peak (or minimum
ventilation rate) per G3.1.3.14.

As required in the comments, the minimum flow setpoint  and required peak
primary air flow , 0.35 W/cfm were put as inputs in e-quest, however despite
making changes, the fan power  has not shown any changes whereas the
Ventilation Fan energy consumption increases. I have attached snap shots of
the input data and no change in the output tab.

Kindly help regarding this and where i am going wrong.

Thanking you in advance.

Regards,
Namrata

-- 
Thanks and Regards ,

Pranati Shroff & Namrata Dhamankar

*a:* Sprout ,Prabaht Printing Works ,
427 Gultekdi, Ind Estate Corner,
2nd Floor, Pune-411037
*m:* 9922215467
*e:  *info at sprout-green.com
projects at sprout-green.com
*w: *www.sprout-green.com <http://www.sprout-green.com>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20190125/1757c66b/attachment.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Query on reviewer comment.docx
Type: application/vnd.openxmlformats-officedocument.wordprocessingml.document
Size: 731527 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20190125/1757c66b/attachment.docx>


More information about the Bldg-sim mailing list