<div dir="ltr"><font face="arial, helvetica, sans-serif">Dear e-Quest users,</font><div><font face="arial, helvetica, sans-serif"><br></font></div><div><font face="arial, helvetica, sans-serif">We have received a review comment for one of our projects stating: From the simulation report
provided (SV-A System Design Parameters report), it does not appear that the
Baseline fans in parallel VAV fan-powered boxes are sized for 50% of peak
primary airflow and modeled with 0.35 W/cfm (0.74 W/L/s) fan power and a
minimum flow setpoint of 30% of peak (or minimum ventilation rate) per
G3.1.3.14.</font></div><div><font face="arial, helvetica, sans-serif"><br></font></div><div><font face="arial, helvetica, sans-serif">As required in the comments, the minimum flow setpoint and required peak primary air flow , 0.35 W/cfm were put as inputs in e-quest, however <span lang="EN-US" style="line-height:115%">despite making changes, the fan power has not shown any changes whereas the Ventilation Fan energy consumption increases. I have attached snap shots of the input data and no change in the output tab.</span></font></div><div><font face="arial, helvetica, sans-serif"><br></font></div><div><font face="arial, helvetica, sans-serif">Kindly help regarding this and where i am going wrong.</font></div><div><font face="arial, helvetica, sans-serif"><br></font></div><div><font face="arial, helvetica, sans-serif">Thanking you in advance.</font></div><div><font face="arial, helvetica, sans-serif"><br></font></div><div><font face="arial, helvetica, sans-serif">Regards,</font></div><div><font face="arial, helvetica, sans-serif" style="">Namrata</font><br><div><div><div><br></div>-- <br><div dir="ltr" class="gmail_signature" data-smartmail="gmail_signature"><div dir="ltr"><div><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><font face="arial black, sans-serif" size="4"><img src="http://www.sprout-green.com/assets/logo.png"></font></div><div><font size="2" face="trebuchet ms, sans-serif">Thanks and Regards ,</font></div><div><font face="arial black, sans-serif" size="4"><br></font></div><div><font size="2" face="tahoma, sans-serif">Pranati Shroff & Namrata Dhamankar </font></div><div><font face="arial black, sans-serif" size="4"><br></font></div><div dir="ltr"><div><span style="color:rgb(68,68,68)"><font style="background-color:rgb(255,255,255)" face="times new roman, serif" size="2"><span style="color:rgb(12,52,61)"><b>a:</b></span> Sprout ,Prabaht Printing Works , </font></span></div><div><span style="color:rgb(68,68,68)"><font style="background-color:rgb(255,255,255)" face="times new roman, serif" size="2">427 Gultekdi, Ind Estate Corner, </font></span></div><div><font color="#444444" face="times new roman, serif" size="2">2nd Floor, Pune-411037</font></div><div><span style="color:rgb(68,68,68)"><font style="background-color:rgb(255,255,255)" face="times new roman, serif" size="2"><span style="color:rgb(12,52,61)"><b>m:</b></span> 9922215467</font></span></div><div><span style="color:rgb(68,68,68)"><font style="background-color:rgb(255,255,255)" face="times new roman, serif" size="2"><b><span style="color:rgb(12,52,61)">e:</span><span style="color:rgb(12,52,61)"> </span> </b><a href="mailto:info@sprout-green.com" target="_blank">info@sprout-green.com</a> <b><br></b><a href="mailto:projects@sprout-green.com" target="_blank">projects@sprout-green.com</a></font></span></div><div><font style="background-color:rgb(255,255,255)" color="#999999" face="times new roman, serif" size="2"><span style="color:rgb(68,68,68)"><b><span style="color:rgb(12,52,61)">w:</span> </b><a href="http://www.sprout-green.com" target="_blank">www.sprout-green.com</a></span><a href="http://www.sprout-green.com" target="_blank"></a></font></div></div></div></div></div></div></div></div></div></div></div></div>