[Bldg-sim] Help Required: Urgent
Sheila Sagerer
ssagerer at comcast.net
Fri Jan 25 08:56:53 PST 2019
Good morning Namrata,
It appears that the Baseline HVAC system is either System 6 or System 8 with PFPB (parallel fan powered boxes). In eQuest, these two system types cannot be modeled using the Pkgd Var Vol or the Variable Air Volume system types; i.e. PFPBs must be modeled as Powered Induction Units.
The 0.35 W/cfm, 50% peak design , and min 30% are then modeled on the Airflow tab at the zone level, not the system (AHU) level in the Zone Terminal and Fans data entry boxes. (Note that these data entry boxes are grayed out for all system types except Powered Induction Units).
When properly modeled, the 0.35 W/cfm and min 30% will show up in the Fan (kW) and Minimum Flow (FRAC) columns on the SV-A reports.
Hope this helps. Thanks, and have a nice day.
Sheila Sagerer, BEMP, LEED AP BD+C | Senior Engineer, Building Optimization Practice
Heapy Engineering | LEED Platinum | 1400 W Dorothy Lane | Dayton OH 45409
(P) 937-224-0861 | www.heapy.com
On Jan 25, 2019, at 7:11 AM, Sprout Info_Mail via Bldg-sim <bldg-sim at lists.onebuilding.org> wrote:
Dear e-Quest users,
We have received a review comment for one of our projects stating: From the simulation report provided (SV-A System Design Parameters report), it does not appear that the Baseline fans in parallel VAV fan-powered boxes are sized for 50% of peak primary airflow and modeled with 0.35 W/cfm (0.74 W/L/s) fan power and a minimum flow setpoint of 30% of peak (or minimum ventilation rate) per G3.1.3.14.
As required in the comments, the minimum flow setpoint and required peak primary air flow , 0.35 W/cfm were put as inputs in e-quest, however despite making changes, the fan power has not shown any changes whereas the Ventilation Fan energy consumption increases. I have attached snap shots of the input data and no change in the output tab.
Kindly help regarding this and where i am going wrong.
Thanking you in advance.
Regards,
Namrata
--
Thanks and Regards ,
Pranati Shroff & Namrata Dhamankar
a: Sprout ,Prabaht Printing Works ,
427 Gultekdi, Ind Estate Corner,
2nd Floor, Pune-411037
m: 9922215467
e: info at sprout-green.com
projects at sprout-green.com
w: www.sprout-green.com
<Query on reviewer comment.docx>
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20190125/205a7863/attachment-0002.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 4186 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20190125/205a7863/attachment-0002.jpg>
More information about the Bldg-sim
mailing list