[TRNSYS-users] Annual Energy Demand

David BRADLEY d.bradley at tess-inc.com
Tue Mar 21 07:20:35 PDT 2023


Htet,

  Welcome to the Trnsys community.

  Trnsys only produces text output files. However, those files can be 
opened in Excel for processing.

  In order to get annual results you will need to use the 
printer/integrator component (Type46). Type46 can be set up (using its 
parameters) to integrate as many inputs as you define over whatever 
period you want. You might look at the example HVAC system projects that 
are located in .\Trnsys18\Examples\HVACTemplates\. You will need to turn 
on the outputs layer in order to see Type46 but once you do, you can see 
how to set up the Type to make integrated summaries. The ones in the 
HVAC template examples are set to create a monthly summary and an hourly 
summary but you can change parameter values to make them do monthly and 
annual summaries.

kind regards,

  David

On 3/20/2023 9:25 PM, Htet Ye Wynn via TRNSYS-users wrote:
> Dear Trnsys Users,
>
> I'm Htet and a beginner in using Trnsys for my research.
> Currently, I'm trying to get the annual cooling load of the building.
> When I run the simulation for the whole year, I can see that the 
> plotter giving me the amount of cooling load fluctuation month by month.
> However, what I want is:
>
>   * I want my result to be printed in a lookup table (like in excel
>     sheet) not in a form of text file.
>   * The summation of cooling load for the whole year.
>
> Thank you very much for taking time to read my email and I really 
> appreciate all your help.
> Thanks in advance.
>
> Regards,
> Htet
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org

-- 
***************************
David BRADLEY
Principal
Thermal Energy System Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI  53703 USA

P:+1.608.274.2577
d.bradley at tess-inc.com

http://www.tess-inc.com
http://www.trnsys.com