[TRNSYS-users] Type 4c

Jeff Thornton thornton at tess-inc.com
Sat Apr 8 07:23:35 PDT 2023


Hadi,

If you have stratification enabled in your storage tank (multiple nodes), and your hot water from solar is going to the top of the tank, and your water that is going to the load is exiting from the top of the tank, then this will happen naturally.  If you want the solar hot water to go directly to the load if it’s hot enough then you’ll need to introduce a series of diverters and mixers, along with appropriate controls, to make that happen.

Jeff/TESS

Sent from my iPhone

> On Apr 8, 2023, at 8:37 AM, Hadi Tannous via TRNSYS-users <trnsys-users at lists.onebuilding.org> wrote:
> 
> 
> Hi
> 
> I am using water tank type 4c for a solar system. The tank is always providing water at the setpoint temperature even when the solar system is providing water at a higher temperature. How can I make the tank provide the water at a temperature higher than the setpoint temperature when that is achieved by the solar system?
> 
> Looking forward to hearing from you 
> 
> 
> Kind regards,
> Hadi 