Hamza,

  I am not aware of a premade example of such a system; however, all of 
the component pieces are available in the standard library. I would 
start by defining the cooling load that the absorption chiller needs to 
meet. What you are trying to cool (whether it is a building modeled 
using Type56 or a data file containing predefined loads) will determine 
which component you choose in order to model the delivery device. As a 
starting point, you can idealize the conditions of the cooling water 
coming into the delivery device(s). From there, work upstream; add the 
absorption chiller and idealize its hot water and cooling water inputs 
using equations or even constant values but connect its chilled water 
loop to the network of delivery devices. Once that is working then you 
can focus on either the solar loop or the cooling tower loop.

kind regards,

  David


On 05/30/2022 10:08, hamza shaikh via TRNSYS-users wrote:
> Does any one have TRNSYS model of solar vapour absorption system? 
> Please send me it is urgent
>
> Thanks in advance
>
> Sent from Yahoo Mail on Android 
> <https://go.onelink.me/107872968?pid=InProduct&c=Global_Internal_YGrowth_AndroidEmailSig__AndroidUsers&af_wl=ym&af_sub1=Internal&af_sub2=Global_YGrowth&af_sub3=EmailSignature>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org

-- 
***************************
David BRADLEY
Principal
Thermal Energy System Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI  53703 USA

P:+1.608.274.2577
d.bradley at tess-inc.com

http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20220531/c5555449/attachment.htm>


More information about the TRNSYS-users mailing list