<p>Hamza,</p>
<p> I am not aware of a premade example of such a system; however,
all of the component pieces are available in the standard library.
I would start by defining the cooling load that the absorption
chiller needs to meet. What you are trying to cool (whether it is
a building modeled using Type56 or a data file containing
predefined loads) will determine which component you choose in
order to model the delivery device. As a starting point, you can
idealize the conditions of the cooling water coming into the
delivery device(s). From there, work upstream; add the absorption
chiller and idealize its hot water and cooling water inputs using
equations or even constant values but connect its chilled water
loop to the network of delivery devices. Once that is working then
you can focus on either the solar loop or the cooling tower loop.</p>
<p>kind regards,</p>
<p> David</p>
<p><br>
</p>
<div class="moz-cite-prefix">On 05/30/2022 10:08, hamza shaikh via
TRNSYS-users wrote:<br>
</div>
<blockquote type="cite"
cite="mid:1129010733.3288511.1653923325653@mail.yahoo.com">
<meta http-equiv="content-type" content="text/html; charset=UTF-8">
Does any one have TRNSYS model of solar vapour absorption system?
Please send me it is urgent
<div><br>
</div>
<div>Thanks in advance<br>
<br>
<div id="ymail_android_signature"><a
id="ymail_android_signature_link"
href="https://go.onelink.me/107872968?pid=InProduct&c=Global_Internal_YGrowth_AndroidEmailSig__AndroidUsers&af_wl=ym&af_sub1=Internal&af_sub2=Global_YGrowth&af_sub3=EmailSignature"
moz-do-not-send="true">Sent from Yahoo Mail on Android</a></div>
</div>
<br>
<fieldset class="moz-mime-attachment-header"></fieldset>
<pre class="moz-quote-pre" wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
</blockquote>
<pre class="moz-signature" cols="72">--
***************************
David BRADLEY
Principal
Thermal Energy System Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI 53703 USA
P:+1.608.274.2577
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
</body>
</html>