You can set the value to whatever you like; the field is in the 
information window for each airnode of the building in TRNBuild. The 
default value (1.2* volume) accounts only for the thermal capacitance of 
the air in the airnode. Typically the default value is multiplied by 
some factor between 5 and 10 to account for the thermal capacitance of 
all the furnishings in the zone.

kind regards,

  David


On 05/16/2022 03:39, Huijie Pu via TRNSYS-users wrote:
>     Hello!
>     In the 05-MultizoneBuilding document, The capacitance will be 
> automatically set to a default value of 1.2*volume. Can the 
> capacitance value be changed to 0.5*volume or 0.8*volume?
>
>
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org

-- 
***************************