<p>You can set the value to whatever you like; the field is in the
information window for each airnode of the building in TRNBuild.
The default value (1.2* volume) accounts only for the thermal
capacitance of the air in the airnode. Typically the default value
is multiplied by some factor between 5 and 10 to account for the
thermal capacitance of all the furnishings in the zone.</p>
<p>kind regards,</p>
<p> David</p>
<p><br>
</p>
<div class="moz-cite-prefix">On 05/16/2022 03:39, Huijie Pu via
TRNSYS-users wrote:<br>
</div>
<blockquote type="cite"
cite="mid:42612eda.38bd.180cc057309.Coremail.huijiepu@163.com">
<meta http-equiv="content-type" content="text/html; charset=UTF-8">
<div
style="line-height:1.7;color:#000000;font-size:14px;font-family:Arial">
<div style="margin:0;">
<div style="margin:0;"> Hello!</div>
<div style="margin:0;"> In the 05-MultizoneBuilding
document, The capacitance will be automatically set to a
default value of 1.2*volume. Can the capacitance value be
changed to 0.5*volume or 0.8*volume?</div>
</div>
<div style="margin:0;"><br>
</div>
</div>
<br>
<br>
<span title="neteasefooter">
<p> </p>
</span><br>
<fieldset class="moz-mime-attachment-header"></fieldset>
<pre class="moz-quote-pre" wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
</blockquote>
<pre class="moz-signature" cols="72">--
***************************
David BRADLEY
Principal
Thermal Energy System Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI 53703 USA
P:+1.608.274.2577
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
</body>
</html>