Jacopo,
You are on the right track with Type690 and a heat pump. The
assumption when generating heating and cooling loads is that the zone
temperature is controlled. The idea of Type690 is to impose those loads
on a lumped capacitance to turn them back into temperatures so that you
can implement a thermostat that controls a heat pump whose energy
addition/removal is also imposed on the lump to try and keep it at a
controlled temperature. The key is to tune the lump so that it reacts to
the load and the input from the heat pump in the same way that the
original zone does.
Another valid approach would be to use Type682. The idea here is that
you impose the heating and cooling loads on a liquid stream. As an
aside, there is also Type693 if you want to impose the loads on an air
stream. The Type682 solution is ideal if you are modeling a central
plant and if your loads include the energy consumption of the terminal
delivery devices. If your heat pumps are zonal then things get a little
more tricky and you're not going to use the heat pumps to directly
impact the liquid stream. Instead you're going to give the heat pump the
entering water temperature and the control mode (heating or cooling).
You're going to use the heat pump's outputs for compressor energy to
modify your zone loads. It sounds more complicated than it is and if you
are using v18 I can make you an example of how it might work.
kind regards,
David
On 05/09/2022 04:44, Jacopo Valente via TRNSYS-users wrote:
>
> Dear TRNSYS users,
>
> I am trying to simulate a system for the conditioning of a building,
> in particular first an air-to-air heat pump system and then a
> water-to-water heat pump system. In my case I haven’t the building
> modeling like using type56, but I have the required loads in both
> heating and cooling mode. I have the tess library and I tried to
> connect the heat pump to the type690, but I'm not sure it's the
> correct choice. Which is the type most suitable for reading the loads
> and controlling the zone temperature?
>
>
> Best regards,
> Jacopo
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
--
***************************
David BRADLEY
Principal
Thermal Energy System Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI 53703 USA
P:+1.608.274.2577
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20220509/d8783584/attachment.htm>
More information about the TRNSYS-users
mailing list