    <p>Jacopo,</p>
    <p> You are on the right track with Type690 and a heat pump. The
      assumption when generating heating and cooling loads is that the
      zone temperature is controlled. The idea of Type690 is to impose
      those loads on a lumped capacitance to turn them back into
      temperatures so that you can implement a thermostat that controls
      a heat pump whose energy addition/removal is also imposed on the
      lump to try and keep it at a controlled temperature. The key is to
      tune the lump so that it reacts to the load and the input from the
      heat pump in the same way that the original zone does.<br>
    </p>
    <p> Another valid approach would be to use Type682. The idea here is
      that you impose the heating and cooling loads on a liquid stream.
      As an aside, there is also Type693 if you want to impose the loads
      on an air stream. The Type682 solution is ideal if you are
      modeling a central plant and if your loads include the energy
      consumption of the terminal delivery devices. If your heat pumps
      are zonal then things get a little more tricky and you're not
      going to use the heat pumps to directly impact the liquid stream.
      Instead you're going to give the heat pump the entering water
      temperature and the control mode (heating or cooling). You're
      going to use the heat pump's outputs for compressor energy to
      modify your zone loads. It sounds more complicated than it is and
      if you are using v18 I can make you an example of how it might
      work.</p>
    <p>kind regards,</p>
    <p> David</p>
    <p><br>
    </p>
    <p><br>
    </p>
    <p>  <br>
    </p>
    <div class="moz-cite-prefix">On 05/09/2022 04:44, Jacopo Valente via
      TRNSYS-users wrote:<br>
    </div>
    <blockquote type="cite"
cite="mid:DB6PR06MB39598F0D381EC3D44E898F34A6C69@DB6PR06MB3959.eurprd06.prod.outlook.com">
      <meta http-equiv="Content-Type" content="text/html; charset=UTF-8">
      <meta name="Generator" content="Microsoft Word 15 (filtered
        medium)">
      <style>@font-face
        {font-family:"Cambria Math";
        panose-1:2 4 5 3 5 4 6 3 2 4;}@font-face
        {font-family:Calibri;
        panose-1:2 15 5 2 2 2 4 3 2 4;}p.MsoNormal, li.MsoNormal, div.MsoNormal
        {margin:0cm;
        font-size:11.0pt;
        font-family:"Calibri",sans-serif;}.MsoChpDefault
        {mso-style-type:export-only;}div.WordSection1
        {page:WordSection1;}</style>
      <div class="WordSection1">
        <p class="MsoNormal">Dear TRNSYS users,<o:p></o:p></p>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal">I am trying to simulate a system for the
          conditioning of a building, in particular first an air-to-air
          heat pump system and then a water-to-water heat pump system.
          In my case I haven’t the building modeling like using type56,
          but I have the required loads in both heating and cooling
          mode. I have the tess library and I tried to connect the heat
          pump to the type690, but I'm not sure it's the correct choice.
          Which is the type most suitable for reading the loads and
          controlling the zone temperature?<o:p></o:p></p>
        <p class="MsoNormal"><br>
          Best regards,<br>
          Jacopo<o:p></o:p></p>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal"><o:p> </o:p></p>
      </div>
      <br>
      <fieldset class="moz-mime-attachment-header"></fieldset>
      <pre class="moz-quote-pre" wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
    </blockquote>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy System Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI  53703 USA

P:+1.608.274.2577
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>