On 2022-03-21 07:01, miriam di matteo via TRNSYS-users wrote:

>  	* First: can you confirm if I understand its functioning? I use it
> only for heating, at the moment.

Your understanding of the model is excellent.  But you made a mistake 
when setting parameter #5; Number of Water Temperatures - Heating.  You 
have set it to 3 in your project when there are 6 water temperatures 
provided in the external data file (25  30  35  40  45  50  
!T_water_in).

Jeff

-- 