[TRNSYS-users] When I set 1st gournd floor as external catagory, what should I set these parameters ?
David BRADLEY
d.bradley at tess-inc.com
Thu Jun 30 06:03:32 PDT 2022
An EXTERNAL floor means that there are ambient conditions on the back
side of the floor of your zone. With an EXTERNAL surface, you'll need to
provide an orientation so that TRNSYS can determine how much solar is
incident on the back (outside the zone) surface. Type56 will also assume
that the temperature and RH of the air on the back side of the surface
are the ambient temperature and RH provided to the model. Bear in mind
that there is no inherent meaning to "GROUND_FLOOR." That is just a name
assigned to a construction.
There are certainly buildings in which all or part of the bottom floor
is above some ambient conditions (perhaps there is an open parking
garage underneath or perhaps part of the building is cantilevered. For
this type of floor, you'd set the "view factor to sky" to 0 because the
back surface of the floor faces the ground and doesn't "see" the sky for
longwave radiation exchange. Geosurf asks for the fraction of the beam
solar radiation that makes it into the zone that strikes the floor. If
your zone is large with relatively few windows you can set that value to
1 thereby assuming that all the beam radiation causes sun patches on the
floor. The surface gains on the inside and outside surfaces should
probably be set to zero. They are a simplified way of modeling radiant
surfaces.
As a side note and if you have not done so already, it might be a good
idea to consult the Type56/TRNBuild documentation, which defines all of
the fields that TRNBuild asks the user to fill in.
kind regards,
David
On 06/28/2022 22:36, H via TRNSYS-users wrote:
> Deal all,
>
> When I set 1st gournd floor as external catagory, what should I set
> these parameters ?
>
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
--
***************************
David BRADLEY
Principal
Thermal Energy System Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI 53703 USA
P:+1.608.274.2577
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20220630/c29a6374/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image.png
Type: image/png
Size: 20543 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20220630/c29a6374/attachment-0001.png>
More information about the TRNSYS-users
mailing list