[TRNSYS-users] Underfloor heating
David BRADLEY
d.bradley at tess-inc.com
Fri Jun 3 11:09:29 PDT 2022
Said,
Thank you for the additional clarification; the layers are not
mirrored by TRNBuild/Type56. Define the construction using the wall
manager and then make sure that the front/back is set in one of the two
zones.
kind regards,
David
On 06/03/2022 11:54, Said LAMGHARI wrote:
> Dear David;
> The picture that I included it is what I'm concerned might be happening.
> in fact the building has two parts. the first one is for adjacent area
> and other it is intended for a ground floor. at the moment I work
> adjacent area.
> Thank you for the precious advice.
> Best.
> Said LAMGHARI
> ------------------------------------------------------------------------
> *De :* David BRADLEY <d.bradley at tess-inc.com>
> *Envoyé :* jeudi 2 juin 2022 20:15
> *À :* Said LAMGHARI <said.lamghari at edu.uca.ma>; TRNSYS users mailing
> list at OneBuilding.org <trnsys-users at lists.onebuilding.org>
> *Objet :* Re: [TRNSYS-users] Underfloor heating
>
> Said,
>
> I am not sure I understand whether you are trying to create a
> construction that has 2 layers of heating tubes or whether you are
> trying to avoid creating such a construction. Can you please clarify
> whether the picture that you included is what you want to model or if
> it is what you are concerned might be happening?
>
>
> In general, an ADJACENT wall (or floor or ceiling) defined in
> TRNBuild does not have any mirroring in it. You create the layers of
> the wall however you wish and then you go to one of the two zones to
> which the wall is adjacent and you set whether that zone contains the
> front or the back of the wall. So if the construction you create is
> made up of the layers: sol, dale, tubes, chape, parquet and you define
> that construction to be ADJACENT (between two zones) then one of the
> zones will have the "sol" face and the other zone will have the
> "parquet" face in it.
>
>
> If, on the other hand, you want to have a construction that has two
> active layers in it you'll need to define something called a "direct
> contact" zone in between them. This is a kind of very low volume
> virtual airnode that sits between two BOUNDARY constructions. Defining
> one can be confusing so if the picture below represents what you want,
> please let me know and I'll try to explain how to do it.
>
>
> Two side notes:
>
>
> 1. the picture you sent seems like it is intended for a ground floor
> rather than for an adjacent floor (given the compacted soil layer). If
> that is indeed the case then you'll want to define the construction as
> a BOUNDARY rather than as ADJACENT.
>
> 2. you're going to need to sandwich the tubing layer between two
> screed (chape) layers. When you are defining the construction enter
> the first screed layer as having half of the actual layer's thickness.
> Next add the active layer and a second screed layer will be added
> below it. You can move the tubing layer up and down in the screed
> layer by adjusting the thickensses of the two adjoining layers but you
> can't put the tubing at the very bottom of the screed layer as it is
> pictured in your drawing.
>
>
> kind regards,
>
> David
>
>
>
> On 06/01/2022 14:48, Said LAMGHARI wrote:
>> Dear David;
>> The creation of a floor or wall is done from the inside to the outside.
>> When I change the construction type of two adjacency room.
>> I notice that it applies to the wall or the ceiling of the other
>> room. I noticed that it is the mirror effect on the adjacency walls.
>> The attached figure shows my idea that I have on the floor study.
>> please confirm this to me, if I m right or not.
>> Best.
>> Said LAMGHARI
>>
>>
>> ------------------------------------------------------------------------
>> *De :* David BRADLEY <d.bradley at tess-inc.com>
>> <mailto:d.bradley at tess-inc.com>
>> *Envoyé :* mercredi 1 juin 2022 15:23
>> *À :* TRNSYS users mailing list at OneBuilding.org
>> <trnsys-users at lists.onebuilding.org>
>> <mailto:trnsys-users at lists.onebuilding.org>
>> *Cc :* Said LAMGHARI <said.lamghari at edu.uca.ma>
>> <mailto:said.lamghari at edu.uca.ma>
>> *Objet :* Re: [TRNSYS-users] Underfloor heating
>>
>> Said,
>>
>> Trnsys tries to mimic what would happen in a real world situation;
>> if you put an active layer into a floor that is also the ceiling of
>> another zone and put hot water through it then the floor/ceiling will
>> heat both the zone above and the zone below. To prevent that from
>> happening, you can put insulation on the side that you do not want to
>> be heated.
>>
>> kind regards,
>>
>> David
>>
>>
>>
>>
>> On 06/01/2022 04:35, Said LAMGHARI via TRNSYS-users wrote:
>>> Dear All,
>>> I have a question about underfloor heating.
>>> Between the floor and the ceiling of two adjacent rooms
>>> (ADJ_ceiling) . Do you have any idea about underfloor heating. since
>>> we will have the mirror effect on this floor so we will have two
>>> active layers..! or not!
>>> Best,
>>> Said LAMGHARI
>>>
>>> _______________________________________________
>>> TRNSYS-users mailing list
>>> TRNSYS-users at lists.onebuilding.org <mailto:TRNSYS-users at lists.onebuilding.org>
>>> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org <http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org>
>> --
>> ***************************
>> David BRADLEY
>> Principal
>> Thermal Energy System Specialists, LLC
>> 3 North Pinckney Street - suite 202
>> Madison, WI 53703 USA
>>
>> P:+1.608.274.2577
>> d.bradley at tess-inc.com <mailto:d.bradley at tess-inc.com>
>>
>> http://www.tess-inc.com <http://www.tess-inc.com>
>> http://www.trnsys.com <http://www.trnsys.com>
> --
> ***************************
> David BRADLEY
> Principal
> Thermal Energy System Specialists, LLC
> 3 North Pinckney Street - suite 202
> Madison, WI 53703 USA
>
> P:+1.608.274.2577
> d.bradley at tess-inc.com <mailto:d.bradley at tess-inc.com>
>
> http://www.tess-inc.com <http://www.tess-inc.com>
> http://www.trnsys.com <http://www.trnsys.com>
--
***************************
David BRADLEY
Principal
Thermal Energy System Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI 53703 USA
P:+1.608.274.2577
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20220603/74faeaa2/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: plancher.png
Type: image/png
Size: 125633 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20220603/74faeaa2/attachment-0001.png>
More information about the TRNSYS-users
mailing list