Ali,

   Types151 and 152 can both heat and cool. In the kind of VAV that 
Types151 and 152 model there is a central unit that can provide heating, 
cooling and reheat. The terminal units can only provide heat/reheat. As 
long as one zone in the whole system requires cooling then the central 
unit has to be in cooling mode. Any zones that require heat will get 
that heat from their own terminal unit boxes. All the terminal boxes 
(except for the one that needs cooling) will back off as much as they 
can (to their minimum air flow rate) and will provide the heat needed. 
If /all/ the zones need heat then the central unit's supply air 
temperature can move upwards.

regards,

  David


On 01/31/2022 15:26, Ali Shahrouzian via TRNSYS-users wrote:
>
> Dear TRNSYS users,
>
> Hi,
>
> I am going to model a VAV air handler system to supply the heating 
> load of a residential building over the course of the winter months. 
> For this purpose, Type 151 and Type 152 components seem most appropriate .
>
> However, I noticed that they are designed (in TRNSYS code) in a way 
> that are only suitable for meeting cooling needs.
>
> I was wondering whether these types (151 and 152) could be used to 
> model a VAV air handler to meet heating demands as well? How?
>
> Best Regards,
>
> Ali
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org

-- 
***************************
David BRADLEY
Principal
Thermal Energy System Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI  53703 USA

P:+1.608.274.2577
d.bradley at tess-inc.com

http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20220131/c6788922/attachment.htm>


More information about the TRNSYS-users mailing list