Karol,
I would suggest sending the project and the files needed to run it to
your distributor. It may be that we need to dig inside the code a bit to
find out exactly what is not converging.
kind regards,
David
On 08/17/2022 03:28, karol.bandurski--- via TRNSYS-users wrote:
>
> Dear David and Arian,
>
> Thank you for your quick response.
>
> 1. Unfortunately changing time step doesn’t help (we change form 1h
> to 5 min).
> 2. We also try switch off internal calculation of convection
> coefficient on ceiling but it not help, moreover it is not
> solution for us as we simulate TABS. However we will switch off
> internal calculation of convection coefficient for windows and
> external walls.
>
> Do you have any other idea?
>
> Do you think that some settings in Control Cards could help (change in
> numerical approach)?
>
> Best,
> Karol
>
> *From:*David BRADLEY <>
> *Sent:* Tuesday, August 16, 2022 8:38 PM
> *To:* TRNSYS users mailing list at OneBuilding.org
> <trnsys-users at lists.onebuilding.org>
> *Cc:* karol.bandurski at put.poznan.pl
> *Subject:* Re: [TRNSYS-users] convergence problems because of high
> ventilation heat flux
>
> Karol,
>
> Check your assumption about the way that the inside heat transfer
> coefficients are being calculated on the zone surfaces. If you have
> allowed the convection coefficients to be internally calculated then
> you can end up with convergence problems inside 56, particularly on
> inside window surfaces and even more particularly if the glass has a
> high u-value.
>
> kind regards,
>
> David
>
> On 08/16/2022 09:50, karol.bandurski--- via TRNSYS-users wrote:
>
> Dear Experts.
>
> We get convergence problem in Type 56. According to our
> investigation source of error is sudden increase of ventilation
> flow in our schedule and ventilation air temperature about 3 K
> lower then room air temperature.
>
> We would like to keep this control schedule and the same time
> avoid convergence problem.
>
> So far we have increase indoor air heat capacity in zones (five
> times), it help a bit.
>
> Do you have any other ideas what we could do?
>
> Should we change something in Control Cards?
>
> Best,
>
> Karol
>
> ---------------------------------------------------------------------------
>
> Karol BANDURSKI Ph.D, Assistant Professor
>
> Faculty of Environmental and Energy Engineering
>
> Division of Heating, Air Conditioning and Air Protection
>
> Poznan University of Technology
>
> https://www.researchgate.net/profile/Karol_Bandurski
> <https://www.researchgate.net/profile/Karol_Bandurski>
>
> ***
>
> dr inż. Karol BANDURSKI, Adiunkt
>
> Wydział Inżynierii Środowiska i Energetyki
>
> Zakład Ogrzewnictwa, Klimatyzacji i Ochrony Powietrza
>
> Politechnika Poznańska
>
>
>
> _______________________________________________
>
> TRNSYS-users mailing list
>
> TRNSYS-users at lists.onebuilding.org
>
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
>
> --
> ***************************
> David BRADLEY
> Principal
> Thermal Energy System Specialists, LLC
> 3 North Pinckney Street - suite 202
> Madison, WI 53703 USA
> P:+1.608.274.2577
> d.bradley at tess-inc.com
> http://www.tess-inc.com
> http://www.trnsys.com
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
--
***************************
David BRADLEY
Principal
Thermal Energy System Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI 53703 USA
P:+1.608.274.2577
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20220817/96fa7613/attachment-0001.htm>
More information about the TRNSYS-users
mailing list