[TRNSYS-users] Error from glazing materials in TRNBUILD
hotline
hotline at Transsolar.com
Fri Sep 10 04:42:37 PDT 2021
Hi Adesanya
the error here is likely not related to the 3D geometry but the optical standard of your window types. We are advising that if you add window data beyond the glazings included in the standard library, you use the Trnsys18.std file to generate the window data. You can find information on this in the Multizone Building Manual c:\TRNSYS18\Documentation\05-MultizoneBuilding.pdf at 5.2.4.6. Definition of a New Window Type
Best regards,
Christina
__________________________________________________________________________________________________
Transsolar KlimaEngineering
Stuttgart | München | Paris | New York
https://www.trnsys.de<https://www.trnsys.de/>
https://transsolar.com/de
<https://www.trnsys.de>
Transsolar Energietechnik GmbH | Curiestraße 2 | 70563 Stuttgart
Geschäftsführer: Matthias Schuler, Thomas Auer, Stefan Holst, Dieter Schnelle
Registered at Amtsgericht Stuttgart HRB 23347 | USt-IdNr.: DE 152272639
The simulation project you have sent will be stored on the local servers of Transsolar Energietechnik GmbH for the duration of the project support. Our employees are obliged by us to confidentiality. After this period, all project-related data is deleted.
The storage of your personal e-mail and other contact information is based on the mutual interest in the execution of this traffic and on a mutual business contact. If you have any questions, please contact our data protection officer at privacy at transsolar.com<mailto:privacy at transsolar.com>. Our privacy policy can be found here<http://www.trnsys.de/docs/userservice/userservice_dataprivacy_en.htm>.
________________________________
Von: TRNSYS-users <trnsys-users-bounces at lists.onebuilding.org> im Auftrag von Misbaudeen Adesanya via TRNSYS-users <trnsys-users at lists.onebuilding.org>
Gesendet: Sonntag, 5. September 2021 15:37
An: trnsys-users at lists.onebuilding.org <trnsys-users at lists.onebuilding.org>
Cc: Misbaudeen Adesanya <misbauadesanya at gmail.com>
Betreff: [TRNSYS-users] Error from glazing materials in TRNBUILD
Dear All,
I am working with a building with multiple zones. After generating the .b18 file from TRNBUILD and uploading it in Type 56. Then running the simulation in TRNSYS, I have this error "inconsistency of optical data standard of glazings within a zone, a different standard was used compared to the previous one. Please check and correct glazing data". I changed the 3D geometry to manual in order to edit the surface it's complaining about (not sure if this is right) but after several attempts, I still don't have a solution.
Can someone please enlighten me as I am new to using this software.
Thank you.
--
Adesanya Misbaudeen Aderemi
Department of Agricultural Civil Engineering
College of Agricultural & Life Sciences
Kyungpook National University
1370 Sangyuk-dong, Puk-gu
Daegu 702-701, South Korea
대구시 북구 산격동 경북대학교 농업토목공학과
Cell phone: +82-10-5168-7503
+234-81-6487-7503
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20210910/22b81906/attachment.htm>
More information about the TRNSYS-users
mailing list