Miriam,

   Are you using the version of Type534 in which all of the tank 
information is taken as parameters or are you using the version in which 
the same information is set by using the plugin? If you are using the 
"all parameters" version you need to look at the parameter list and make 
sure that the value of parameter 41 makes sense (it might contain a 
negative number for specific heat or an efficiency greater than 1). If 
you are using the plugin version then send your project and the tank 
data file (referenced in the proforma) to your distributor and they can 
help find the offending value.

kind regards,

  David


On 11/02/2021 05:47, miriam di matteo via TRNSYS-users wrote:
> Hi all,
> I try to simulate a system with a HP (type 941) and a Boiler(type) 
> that exchange heat with a storage tank (type 534). But i have this error:
>
> TRNSYS Message    103 : The TRNSYS TYPE checking routine has found an 
> inconsistency in the specified component between the input file and 
> the information expected by the Type
>
> Reported information  : An illegal PARAMETER value has been reported 
> by the model. The model has reported that Parameter 41 is the problem 
> - but this may not be the case. Please check the component configuration.
>
> But i don't understand how resolve this problem.
> can anyone help me, or give me any advice on this?
>
> thanks a lot in advance.
> Miriam
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org

-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI  53703 USA

P:+1.608.274.2577
d.bradley at tess-inc.com

http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20211102/da6ada0b/attachment.htm>


More information about the TRNSYS-users mailing list