Christina,
Thanks for responding to this with such a comprehensive explanation!
David
On 03/17/2021 04:20, hotline via TRNSYS-users wrote:
> Hi Toni,
>
> you said you are using an internal shading factor for the adjacent
> window, right? In contrast to external shading, which just uses a
> simple factor to determine the shading (ESHADE = 1 -> Transmission =
> 0), internal shading is modelling much more detailed effects, see
> image below:
>
>
> Of all the radiation coming in through the window, a part is absorbed
> by the shading device and then released to the airnode through
> convection, some is reflected towards the window, again there we have
> absorption, convection and reflection back towards the zone and so on.
> Therefore, an internal shading device can never prevent all solar
> gains from entering a zone. Please see /5.2.4.6. Definition of a New
> Window Type /and /5.4.2.9. External and Internal Shading Devices /of
> the Multizone Building part in the TRNSYS Documentation for more info
> on this.
>
> Best regards,
> Christina
>
> /__________________________________________________________________________________________________/
>
> **
>
> *Transsolar KlimaEngineering*
>
> Stuttgart | München | Paris | New York
>
> Transsolar Energietechnik GmbH | Curiestraße 2 | 70563 Stuttgart
>
> Geschäftsführer: Matthias Schuler, Thomas Auer, Stefan Holst, Dieter
> Schnelle
>
> Registered at Amtsgericht Stuttgart HRB 23347 | USt-IdNr.: DE 152272639
>
> The simulation project you have sent will be stored on the local
> servers of Transsolar Energietechnik GmbH for the duration of the
> project support. Our employees are obliged by us to confidentiality.
> After this period, all project-related data is deleted.
>
> The storage of your personal e-mail and other contact information is
> based on the mutual interest in the execution of this traffic and on a
> mutual business contact. If you have any questions, please contact our
> data protection officer at privacy at transsolar.com
> <mailto:privacy at transsolar.com>. Our privacy policy can be found here
> <http://www.trnsys.de/docs/userservice/userservice_dataprivacy_en.htm>.
>
>
> ------------------------------------------------------------------------
> *Von:* TRNSYS-users <trnsys-users-bounces at lists.onebuilding.org> im
> Auftrag von Toni Calabrese via TRNSYS-users
> <trnsys-users at lists.onebuilding.org>
> *Gesendet:* Dienstag, 16. März 2021 18:00
> *An:* TRNSYS users mailing list at OneBuilding.org
> <trnsys-users at lists.onebuilding.org>
> *Cc:* Toni Calabrese <toni.calabrese at ost.ch>
> *Betreff:* [TRNSYS-users] Problem with adjacent window
>
> Hi,
>
> I am working in Trnsys18. I have a building model with two thermal
> zones (Wintergarten and one room) with an external window for the
> wintergarten and an adjacent window between the two zones. If I set
> the external shading factor of the external window to 1, I have no
> solar gains in the two zones, as it should be -> CORRECT!
>
> I tried then to shade just the adjacent window between the two zones
> (int. shading factor of 1 in TRNBUILD) and I expected solar gains just
> in the wintergarten, but not in the room. I got solar gains in both
> zones. It seems that I am not able to shade completely just the
> adjacent window.
>
> Which is the problem?
>
> ------------------------------------------------------------------------
>
> *Toni Calabrese*, MSc.
>
> Wissenschaftlicher Projektleiter
>
> toni.calabrese at spf.ch <mailto:toni.calabrese at spf.ch>
> |toni.calabrese at ost.ch <mailto:toni.calabrese at ost.ch>
>
> T +41 58 257 4827
>
> SPF Institut für Solartechnik
>
> OST – Ostschweizer Fachhochschule
>
> Oberseestr. 10 | CH-8640 Rapperswil | Switzerland | _www.spf.ch
> <http://www.spf.ch/>_| _www.ost.ch <http://www.ost.ch/>_
>
> OST – Ostschweizer Fachhochschule ist der Zusammenschluss aus FHS
> St.Gallen, HSR Rapperswil und NTB Buchs.
>
> *Kursmodul Energiespeicher (4 Tage) an der OST – Rapperswil:*
>
> Alles was Sie zu thermischen, elektrischen, chemischen und
> mechanischen Energiespeichern wissen müssen:
>
> Do. 20.05. / Fr. 21.05. / Do. 27.05. / Fr. 28.05.
>
> Jetzt hier
> <https://www.ost.ch/de/event/article/energiespeicher-theorie-und-anwendungen-4-kurstage/>
> anmelden
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI 53703 USA
P:+1.608.274.2577
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20210317/cbeb18f6/attachment-0001.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image.png
Type: image/png
Size: 70068 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20210317/cbeb18f6/attachment-0003.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.png
Type: image/png
Size: 125136 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20210317/cbeb18f6/attachment-0004.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image005.png
Type: image/png
Size: 11767 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20210317/cbeb18f6/attachment-0005.png>
More information about the TRNSYS-users
mailing list