[TRNSYS-users] How to get constant outlet temperature from heat pump
Jeff Thornton
thornton at tess-inc.com
Thu Jul 29 09:24:49 PDT 2021
Amirezza,
1) Most times you don't try and get a constant outlet temperature out of
a heat pump (unless you have a variable speed heat pump) - you simply
charge the storage tank using an on/off controller that watches the tank
temperature and then you use a tempering valve on the load side to
deliver the correct temperature water; bypassing some of the return
water from the load around the tank and mixing with a fraction that goes
through the tank.
2) I don't see any pipes in your flow loops. Please consider adding them
to allow for some thermal capacitance in the loops which will help
control the system and provide more reasonable results.
Jeff
---
Jeff Thornton
President - TESS LLC
3 N. Pinckney Street, Suite 202, Madison WI USA 53703
Office: (608) 274-2577 Fax: (608) 278-1475
www.tess-inc.com
E-Mail: thornton at tess-inc.com
On 07/29/2021 2:46 am, Amirreza Heidari via TRNSYS-users wrote:
> Hello,
>
> I have a heat pump (type 938) that supplies hot water to two tanks, one for space heating and the other for domestic hot water. Because the return temperature of the hot water is varying a lot (from 50 C to 90 C), the outlet temperature of hat pump also varies a lot. I am designing a control method that only works based on turning ON and OFF the heat pump and supply pumps to adjust the temperature of building and hot water tank. The variations of heat pump outlet temperature has made the control process much more complicated and less efficient. I can use an auxiliary heater at the outlet of heat pump to make sure a constant outlet temperature, but this kind of heaters are not very energy efficient and I would avoid using them as much as possible. Is there any other way to make sure that my heat pump would produce a constant outlet temperature regardless of inlet temperature?
>
> Thanks
>
> --------------------------------------------------------------------------------------------------------------------------------------------------
>
> AMIRREZA HEIDARI
> _Department of Energy Engineering_
> _Sharif University of Technology_
> _Tehran-Iran_
> _E-mail address_:
>
>> heidari at energy.sharif.edu
>
>> amirrezaheidarysbu at gmail.com
>
> P_ __SAVE A TREE... PLEASE DON'T PRINT THIS E-MAIL UNLESS YOU REALLY NEED TO._
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org [1]
Links:
------
[1]
http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20210729/0d03f330/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image.png
Type: image/png
Size: 81348 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20210729/0d03f330/attachment-0002.png>
More information about the TRNSYS-users
mailing list