Habtamu,

  That is the correct method. I usually define a gain in TRNBuild that 
is called "QRADIATOR" and that sets the split between how much of the 
gain is convective and how much is radiative. Although we call them 
"radiators" usually about 80% of their heat gain is convective. So my 
QRADIATOR has 0.8 set as its convective part and 0.2 set for its 
radiative part. Then in each zone, I select that QRADIATOR gain and I 
scale it by the input value that comes from Type1231.

If you are not seeing as much heat output as you expect from your 
radiator recall that usually the design heat output assumes an air 
temperature of about 10C. If you then try to maintain something more 
like 20C in the zone then the radiator will not put out anywhere near 
the design heat amount. It will put out measurably less.

kind regards,

  David


On 12/07/2021 10:25, Habtamu Tkubet via TRNSYS-users wrote:
> Dear David
> Hope you are doing well and safe. I appreciate your support in 
> answering all related questions in TRNSYS. I have tried to type 1231 
> radiator for my two-store building type56 in order to give a heating 
> system for a room of 13*7*3.8m on the ground floor, however, still, I 
> am not sure enough on the result.
> let me explain, some of the steps I followed to model the system
> 1. I added Radiator as miscellaneous in TRNBuild gain/loss and 
> considering in the convective  "1*input"
> 2. I connected each radiator output of "Heat Transfer" to the type56 
> to Input
> image.png
> and the zone temperature to the input of the radiator temperature
>
> image.png
> let me know if I am going in the right way?
>
>
> -- 
> ------------------------------------------------------------------------------------------------------
> Habtamu Tkubet
> Doctorant
> /Université de Lorraine/
> Faculté des Sciences & Technologies - LERMAB and CRAN
>  Epinal, France
> Tél :+2519 11 79 05 22 /773623147
> email:- habtish20002 at gmail.com 
> <http://habtish20002gmail.com/>;habtamu-tkubet.ebuy at unvi-lorraine.fr
> <mailto:habtamu-tkubet.ebuy at unvi-lorraine.fr>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org

-- 
***************************
David BRADLEY
Principal
Thermal Energy System Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI  53703 USA

P:+1.608.274.2577
d.bradley at tess-inc.com

http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20211208/c717676e/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image.png
Type: image/png
Size: 5466 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20211208/c717676e/attachment-0004.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image.png
Type: image/png
Size: 58142 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20211208/c717676e/attachment-0005.png>


More information about the TRNSYS-users mailing list