[TRNSYS-users] Type58 quality of steam
thornton at tess-inc.com
thornton at tess-inc.com
Wed Aug 25 11:33:16 PDT 2021
On 2021-08-25 08:33, Tushar Sharma via TRNSYS-users wrote:
> I have a question with regards to the output "Quality of the state" of
> Type58 as can be seen below. I am using steam (Prameter1 value = 718)
> for this model and the ideal value should be between 0 (water) and 1
> (dry saturated steam). But what I get is strange values ranging from
> -800 to +999.
The quality of steam ranges from 0 to 1 for steam in the saturation
region as you suggest. However for sub-cooled steam, or superheated
steam, the quality of the steam isn't defined. So a value less than
zero signifies subcooled steam and a value greater than 1 signifies
superheated steam. The magnitude of the results above 1 or below zero
is irrelevant.
Jeff
--