[TRNSYS-users] Heating Type Manager (Heating Load is too high)

David BRADLEY d.bradley at tess-inc.com
Wed Nov 25 15:23:56 PST 2020


Asma,

  Take a look at the ground floor boundary condition. Depending on 
whether you used the building wizard or not, the temperature of the 
ground underneath the slab can default to 0C, which often causes 
unrealistically high heating loads and unrealistically low cooling loads.

kind regards,

  David



On 11/25/2020 09:52, Asma Sohail via TRNSYS-users wrote:
> Hello Christina,
>
> thank you for the quick reply. Yes you're right, I'm converting the 
> Qsens only from kJ/hr to W. I then enter the values ​​in Excel and 
> divide my total heating load from a zone by the zone-area. I have a 
> problem especially with the zone 15 and zone 16. These are interior 
> rooms. An elevator and installation shaft (no heating on) is adjacent 
> to these rooms. The elevator and installation shaft do not fall below 
> a temperature of 15 degrees, so it's impossible that the zone 15 and 
> zone 16 needs that much of heating power I get in the simulation. I 
> even calculated the heat load manually. I don't know why, but I only 
> get for interior zones a heat load that is way to high. There's 
> somewhere a problem, maybe it's an easy problem, but I do not find it. 
> I checked every link and the .b18-file but I do not find it. I also 
> have to say, it's my first time working with TRNSYS. Perhaps the 
> problem is in some setting I did wrong.. I hope really you could help 
> me. Thank you in advance for your time, effort and help.
>
> Best regards,
>
> Asma
>
> ------------------------------------------------------------------------
> *Von:* Sohail, Asma <st159047 at stud.uni-stuttgart.de>
> *Gesendet:* Mittwoch, 25. November 2020 07:25
> *An:* asma.sohail at hotmail.de <asma.sohail at hotmail.de>
> *Betreff:* WG: Heating Type Manager (Heating Load is too high)
> *
> *
> ------------------------------------------------------------------------
> *Von:* TRNSYS-usersIm Auftrag vonhotline via TRNSYS-users
> *Gesendet:* Mittwoch, 25. November 2020 03:24:44 (UTC-12:00) 
> Internationale Datumsgrenze West
> *An:* TRNSYS users mailing list at OneBuilding.org
> *Cc:* hotline
> *Betreff:* Re: [TRNSYS-users] Heating Type Manager (Heating Load is 
> too high)
>
> Hello Asma,
>
> I had a quick look at your .tpf-File and it seems that you are using 
> the Qsens output from the building, converting these in the Equations 
> "Q_sens" and then plotting them, right? The building outputs come in 
> kJ/hr, so in the equation you're only converting them to W, not W/m². 
> I didn't check the project in detail though, so i don't know if that 
> accounts for all of the difference.
>
> I hope this helps, let me know if it is a different problem.
>
> Best,
> Christina
>
> ------------------------------------------------------------------------
> *Von:* TRNSYS-users <trnsys-users-bounces at lists.onebuilding.org> im 
> Auftrag von Asma Sohail via TRNSYS-users 
> <trnsys-users at lists.onebuilding.org>
> *Gesendet:* Mittwoch, 25. November 2020 14:15
> *An:* trnsys-users at lists.onebuilding.org 
> <trnsys-users at lists.onebuilding.org>
> *Cc:* Asma Sohail <asma.sohail at hotmail.de>
> *Betreff:* [TRNSYS-users] Heating Type Manager (Heating Load is too high)
> Hello trnsys-users,
>
> this is Asma from the University of Stuttgart. Right now I'm working 
> at my diploma thesis using TRNSYS and a problem occured we were not 
> able to solve yet. I hope that you might have a solution or an idea 
> how to fix it. In TRNBuild I'm using the Heating Type Manager with 
> unlimited power to heat a room to a  certain temperature (20°C). I'm 
> only using convective heat. But something is not working properly with 
> the simulation. I get a heating load that is far too high for certain 
> rooms. Specifically, it is about interior rooms with a too high 
> heating load. I've already checked all links or sources of error, but 
> haven't found anything that causes an error. My maximum specific 
> heating load should actually be around 40 W / m² (144 kJ / h per m²), 
> but I get around 100 W/m² (360 kJ/h per m²), although the outside 
> temperature does not fall into the minus range. It would be great if 
> you had an idea
> how to fix that or if you could identify the problem. Thank you very 
> much in advance!! I attached the files I used in case you have time to 
> have a look at them.
>
> Thanks and kind regards
>
> Asma
>
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org

-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com

http://www.tess-inc.com
http://www.trnsys.com

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20201125/8fe91446/attachment.html>


More information about the TRNSYS-users mailing list