    <p>Asma,</p>
    <p> Take a look at the ground floor boundary condition. Depending on
      whether you used the building wizard or not, the temperature of
      the ground underneath the slab can default to 0C, which often
      causes unrealistically high heating loads and unrealistically low
      cooling loads.</p>
    <p>kind regards,</p>
    <p> David</p>
    <p><br>
    </p>
    <p><br>
    </p>
    <div class="moz-cite-prefix">On 11/25/2020 09:52, Asma Sohail via
      TRNSYS-users wrote:<br>
    </div>
    <blockquote type="cite"
cite="mid:AM0PR09MB3826242A74935C8EDEEB7A878FFA0@AM0PR09MB3826.eurprd09.prod.outlook.com">
      <meta http-equiv="Content-Type" content="text/html; charset=UTF-8">
      <style type="text/css" style="display:none;"> P {margin-top:0;margin-bottom:0;}</style>
      <div style="font-family: Calibri, Helvetica, sans-serif;
        font-size: 12pt; color: rgb(0, 0, 0);">
        Hello Christina,</div>
      <div style="font-family: Calibri, Helvetica, sans-serif;
        font-size: 12pt; color: rgb(0, 0, 0);">
        <br>
      </div>
      <div style="font-family: Calibri, Helvetica, sans-serif;
        font-size: 12pt; color: rgb(0, 0, 0);">
        thank you for the quick reply. Yes you're right, I'm converting
        the Qsens only from kJ/hr to W. I then enter the values ​​in
        Excel and divide my total heating load from a zone by the
        zone-area. I have a problem especially with the zone 15 and zone
        16. These are interior rooms. An elevator and installation shaft
        (no heating on) is adjacent to these rooms. The elevator and
        installation shaft do not fall below a temperature of 15
        degrees, so it's impossible that the zone 15 and zone 16 needs
        that much of heating power I get in the simulation. I even
        calculated the heat load manually. I don't know why, but I only
        get for interior zones a heat load that is way to high. There's
        somewhere a problem, maybe it's an easy problem, but I do not
        find it. I checked every link and the .b18-file but I do not
        find it. I also have to say, it's my first time working with
        TRNSYS. Perhaps the problem is in some setting I did wrong.. I
        hope really you could help me. Thank you in advance for your
        time, effort and help.</div>
      <div style="font-family: Calibri, Helvetica, sans-serif;
        font-size: 12pt; color: rgb(0, 0, 0);">
        <br>
      </div>
      <div style="font-family: Calibri, Helvetica, sans-serif;
        font-size: 12pt; color: rgb(0, 0, 0);">
        Best regards,</div>
      <div style="font-family: Calibri, Helvetica, sans-serif;
        font-size: 12pt; color: rgb(0, 0, 0);">
        <br>
      </div>
      <div style="font-family: Calibri, Helvetica, sans-serif;
        font-size: 12pt; color: rgb(0, 0, 0);">
        Asma</div>
      <div>
        <div style="font-family:Calibri,Helvetica,sans-serif;
          font-size:12pt; color:rgb(0,0,0)">
          <br>
        </div>
        <hr tabindex="-1" style="display:inline-block; width:98%">
        <div id="divRplyFwdMsg" dir="ltr"><font style="font-size:11pt"
            face="Calibri, sans-serif" color="#000000"><b>Von:</b>
            Sohail, Asma <a class="moz-txt-link-rfc2396E" href="mailto:st159047@stud.uni-stuttgart.de"><st159047@stud.uni-stuttgart.de></a><br>
            <b>Gesendet:</b> Mittwoch, 25. November 2020 07:25<br>
            <b>An:</b> <a class="moz-txt-link-abbreviated" href="mailto:asma.sohail@hotmail.de">asma.sohail@hotmail.de</a>
            <a class="moz-txt-link-rfc2396E" href="mailto:asma.sohail@hotmail.de"><asma.sohail@hotmail.de></a><br>
            <b>Betreff:</b> WG: Heating Type Manager (Heating Load is
            too high)</font>
          <div> </div>
        </div>
        <div dir="ltr"><strong>
            <div><font size="2" face="Tahoma" color="#000000"> </font></div>
          </strong>
          <hr tabindex="-1" style="display:inline-block; width:98%">
          <font size="2" face="Tahoma"><b>Von:</b> TRNSYS-usersIm
            Auftrag vonhotline via TRNSYS-users<br>
            <b>Gesendet:</b> Mittwoch, 25. November 2020 03:24:44
            (UTC-12:00) Internationale Datumsgrenze West<br>
            <b>An:</b> TRNSYS users mailing list at OneBuilding.org<br>
            <b>Cc:</b> hotline<br>
            <b>Betreff:</b> Re: [TRNSYS-users] Heating Type Manager
            (Heating Load is too high)<br>
          </font><br>
          <div>
            <div style="font-family:Calibri,Arial,Helvetica,sans-serif;
              font-size:12pt; color:rgb(0,0,0)">
              Hello Asma, </div>
            <div style="font-family:Calibri,Arial,Helvetica,sans-serif;
              font-size:12pt; color:rgb(0,0,0)">
              <br>
            </div>
            <div style="font-family:Calibri,Arial,Helvetica,sans-serif;
              font-size:12pt; color:rgb(0,0,0)">
              I had a quick look at your .tpf-File and it seems that you
              are using the Qsens output from the building, converting
              these in the Equations "Q_sens" and then plotting them,
              right? The building outputs come in <span
                style="background-color:rgb(255,255,255);
                display:inline!important">kJ/hr, so in the equation
                you're only converting them to W, not W/m². I didn't
                check the project in detail though, so i don't know if
                that accounts for all of the difference.</span></div>
            <div style="font-family:Calibri,Arial,Helvetica,sans-serif;
              font-size:12pt; color:rgb(0,0,0)">
              <span style="background-color:rgb(255,255,255);
                display:inline!important"><br>
              </span></div>
            <div style="font-family:Calibri,Arial,Helvetica,sans-serif;
              font-size:12pt; color:rgb(0,0,0)">
              <span style="background-color:rgb(255,255,255);
                display:inline!important">I hope this helps, let me know
                if it is a different problem.</span></div>
            <div style="font-family:Calibri,Arial,Helvetica,sans-serif;
              font-size:12pt; color:rgb(0,0,0)">
              <span style="background-color:rgb(255,255,255);
                display:inline!important"><span><br>
                </span></span></div>
            <div style="font-family:Calibri,Arial,Helvetica,sans-serif;
              font-size:12pt; color:rgb(0,0,0)">
              <span style="background-color:rgb(255,255,255);
                display:inline!important"><span>Best, </span></span></div>
            <div style="font-family:Calibri,Arial,Helvetica,sans-serif;
              font-size:12pt; color:rgb(0,0,0)">
              <span style="background-color:rgb(255,255,255);
                display:inline!important"><span>Christina </span></span></div>
            <div style="font-family:Calibri,Arial,Helvetica,sans-serif;
              font-size:12pt; color:rgb(0,0,0)">
              <br>
            </div>
            <hr tabindex="-1" style="display:inline-block; width:98%">
            <div id="x_divRplyFwdMsg" dir="ltr"><font
                style="font-size:11pt" face="Calibri, sans-serif"
                color="#000000"><b>Von:</b> TRNSYS-users
                <a class="moz-txt-link-rfc2396E" href="mailto:trnsys-users-bounces@lists.onebuilding.org"><trnsys-users-bounces@lists.onebuilding.org></a> im
                Auftrag von Asma Sohail via TRNSYS-users
                <a class="moz-txt-link-rfc2396E" href="mailto:trnsys-users@lists.onebuilding.org"><trnsys-users@lists.onebuilding.org></a><br>
                <b>Gesendet:</b> Mittwoch, 25. November 2020 14:15<br>
                <b>An:</b> <a class="moz-txt-link-abbreviated" href="mailto:trnsys-users@lists.onebuilding.org">trnsys-users@lists.onebuilding.org</a>
                <a class="moz-txt-link-rfc2396E" href="mailto:trnsys-users@lists.onebuilding.org"><trnsys-users@lists.onebuilding.org></a><br>
                <b>Cc:</b> Asma Sohail <a class="moz-txt-link-rfc2396E" href="mailto:asma.sohail@hotmail.de"><asma.sohail@hotmail.de></a><br>
                <b>Betreff:</b> [TRNSYS-users] Heating Type Manager
                (Heating Load is too high)</font>
              <div> </div>
            </div>
            <div dir="ltr">
              <div style="font-family:Calibri,Helvetica,sans-serif;
                font-size:12pt; color:rgb(0,0,0)">
                Hello trnsys-users,</div>
              <div style="font-family:Calibri,Helvetica,sans-serif;
                font-size:12pt; color:rgb(0,0,0)">
                <br>
              </div>
              <div style="font-family:Calibri,Helvetica,sans-serif;
                font-size:12pt; color:rgb(0,0,0)">
                this is Asma from the University of Stuttgart. Right now
                I'm working at my diploma thesis using TRNSYS and a
                problem occured we were not able to solve yet. I hope
                that you might have a solution or an idea how to fix it.
                In TRNBuild I'm using the Heating Type Manager with
                unlimited power to heat a room to a  certain temperature
                (20°C). I'm only using convective heat. But something is
                not working properly with the simulation. I get a
                heating load that is far too high for certain
                rooms. Specifically, it is about interior rooms with a
                too high heating load. I've already checked all links or
                sources of error, but haven't found anything that causes
                an error. My maximum specific heating load should
                actually be around 40 W / m² (144 kJ / h per m²), but I
                get around 100 W/m² (360 kJ/h per m²), although the
                outside temperature does not fall into the minus
                range. It would be great if you had an idea
                <div>how to fix that or if you could identify the
                  problem. Thank you very much in <span
                    style="color:rgb(0,0,0);
                    font-family:Calibri,Helvetica,sans-serif;
                    font-size:12pt">advance!! </span><span
                    style="color:rgb(0,0,0);
                    font-family:Calibri,Helvetica,sans-serif;
                    font-size:12pt">I attached the files I used in case
                    you have time to have a look at them.</span></div>
              </div>
              <div style="font-family:Calibri,Helvetica,sans-serif;
                font-size:12pt; color:rgb(0,0,0)">
                <br>
              </div>
              <div style="font-family:Calibri,Helvetica,sans-serif;
                font-size:12pt; color:rgb(0,0,0)">
                Thanks and kind regards</div>
              <div style="font-family:Calibri,Helvetica,sans-serif;
                font-size:12pt; color:rgb(0,0,0)">
                <br>
              </div>
              <div style="font-family:Calibri,Helvetica,sans-serif;
                font-size:12pt; color:rgb(0,0,0)">
                Asma </div>
              <div style="font-family:Calibri,Helvetica,sans-serif;
                font-size:12pt; color:rgb(0,0,0)">
                <br>
              </div>
              <div style="font-family:Calibri,Helvetica,sans-serif;
                font-size:12pt; color:rgb(0,0,0)">
                <pre><pre>
</pre>
</pre>
              </div>
            </div>
          </div>
        </div>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <pre class="moz-quote-pre" wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
    </blockquote>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>