[TRNSYS-users] Schedule for days, weeks and months

David BRADLEY d.bradley at tess-inc.com
Thu Aug 13 07:55:27 PDT 2020


Dr. Bina,

  There are two kinds of division by zero errors. If you're getting one 
that is being reported by TRNSYS in the error/warning log then make sure 
that any equations you have in your input file are written like:

myEquation = 1/MAX(myVariable,0.)

The other kind of division by zero error is an ugly unhandled one that 
comes up in a popup window over top of your online plotter. If that is 
the kind that you are getting then please send the project and any 
additional files needed to run it to your distributor. They'll need to 
get into the code to find the cause of the error.

kind regards,

  David


On 08/13/2020 09:40, saeid mohammadzadeh wrote:
> Dear Dr. David;
> Thank you so much for your reply. I finally found a way but still 
> does not work for the cooling condition. I made seasonally and hourly 
> forcing files and connected them as an input file to my building (as 
> you mentions in this email also). But unfortunately for cooling give 
> the error of division by zero...
> Another way is using an excel file but again in the cooling does not 
> work and I think it is because of the zeros in the days, weekends, and 
> no airconditioning seasons.
>
> //Best Regards//
> /Saeid Mohammadzadeh Bina, Dr. (Eng.)/
> //-------------------------------------------------//
> /Akita University/
> /Graduate school of International Resource Sciences//.
> 1-1 Tegata gakuen-machi, Akita 010-8502, Japan/
> /Tel: //+815068665026 (Japan)/
> / +989141011757 (Iran)///
> /E-mail: //d9515254 at s.akita-u.ac.jp/ 
> <mailto:s.mohammadzadeh66 at gmail.com>//
> /mohammadzadehsaeid at yahoo.com <mailto:mohammadzadehsaeid at yahoo.com>/
> //-------------------------------------------------
>
> //
>
>
> On Thu, Aug 13, 2020 at 11:32 PM David BRADLEY <d.bradley at tess-inc.com 
> <mailto:d.bradley at tess-inc.com>> wrote:
>
>     Dr Bina,
>
>       If you have access to the TESS Applications Library, you can
>     define such schedules using the Types in that library. In TRNBuild
>     you will need to select that the schedule values will come from
>     INPUTS instead of from SCHEDULES that are defined inside TRNBuild.
>
>     best,
>
>      David
>
>
>     On 08/12/2020 23:12, saeid mohammadzadeh via TRNSYS-users wrote:
>>     Hello dear TRNSYS users;
>>
>>     I have a question regarding the schedule for heating and cooling:
>>     Firstly, I want to calculate the heating and cooling loads using
>>     the energy balance method (just on the heating the cooling
>>     buttons) based on the following time table:
>>     For weekdays from 8 to 18 (either cooling or heating);
>>     For the weekends off (either cooling or heating);
>>     From Nov. to April "Heating";
>>     From Jul. to Sep. "Cooling".
>>     Secondly, I would like to use this schedule and also
>>     thermostat (either schedule or zone temperature is 1 for heating
>>     or cooling) to command the airconditioning system that I will add
>>     later.
>>
>>     And another issue, which is not important now, on weekdays later
>>     I want to use complex timing (8 to 18 full occupancy and other
>>     hours ratio of office workers).
>>
>>     //Best Regards//
>>     /Saeid Mohammadzadeh Bina, Dr. (Eng.)/
>>     //-------------------------------------------------//
>>     /Akita University/
>>     /Graduate school of International Resource Sciences//.
>>     1-1 Tegata gakuen-machi, Akita 010-8502, Japan/
>>     /Tel: //+815068665026 (Japan)/
>>     / +989141011757 (Iran)///
>>     /E-mail: //d9515254 at s.akita-u.ac.jp/
>>     <mailto:s.mohammadzadeh66 at gmail.com>//
>>     /mohammadzadehsaeid at yahoo.com <mailto:mohammadzadehsaeid at yahoo.com>/
>>     //-------------------------------------------------
>>
>>     //
>>
>>     _______________________________________________
>>     TRNSYS-users mailing list
>>     TRNSYS-users at lists.onebuilding.org  <mailto:TRNSYS-users at lists.onebuilding.org>
>>     http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
>
>     -- 
>     ***************************
>     David BRADLEY
>     Principal
>     Thermal Energy Systems Specialists, LLC
>     3 North Pinckney Street - suite 202
>     Madison, WI  53703 USA
>
>     P:+1.608.274.2577
>     F:+1.608.278.1475
>     d.bradley at tess-inc.com  <mailto:d.bradley at tess-inc.com>
>
>     http://www.tess-inc.com
>     http://www.trnsys.com
>
-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com

http://www.tess-inc.com
http://www.trnsys.com

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20200813/a3285875/attachment-0001.html>


More information about the TRNSYS-users mailing list