    <p>Dr. Bina,</p>
    <p> There are two kinds of division by zero errors. If you're
      getting one that is being reported by TRNSYS in the error/warning
      log then make sure that any equations you have in your input file
      are written like:</p>
    <p>myEquation = 1/MAX(myVariable,0.)</p>
    <p>The other kind of division by zero error is an ugly unhandled one
      that comes up in a popup window over top of your online plotter.
      If that is the kind that you are getting then please send the
      project and any additional files needed to run it to your
      distributor. They'll need to get into the code to find the cause
      of the error.</p>
    <p>kind regards,</p>
    <p> David</p>
    <p><br>
    </p>
    <div class="moz-cite-prefix">On 08/13/2020 09:40, saeid
      mohammadzadeh wrote:<br>
    </div>
    <blockquote type="cite"
cite="mid:CABCqxALPtYmwnwvh2FMUBb=b6MEXjR3mpJdAoO8QZ6RPFjxsvg@mail.gmail.com">
      <meta http-equiv="content-type" content="text/html; charset=UTF-8">
      <div dir="ltr">
        <div class="gmail_default"
          style="font-family:arial,helvetica,sans-serif;font-size:small">Dear
          Dr. David;</div>
        <div class="gmail_default"
          style="font-family:arial,helvetica,sans-serif;font-size:small">Thank
          you so much for your reply. I finally found a way but still
          does not work for the cooling condition. I made seasonally and
          hourly forcing files and connected them as an input file to my
          building (as you mentions in this email also). But
          unfortunately for cooling give the error of division by
          zero...</div>
        <div class="gmail_default"
          style="font-family:arial,helvetica,sans-serif;font-size:small">Another
          way is using an excel file but again in the cooling does not
          work and I think it is because of the zeros in the days,
          weekends, and no airconditioning seasons.</div>
        <div class="gmail_default"
          style="font-family:arial,helvetica,sans-serif;font-size:small"><br>
        </div>
        <div class="gmail_default"
          style="font-family:arial,helvetica,sans-serif;font-size:small"><i
style="color:rgb(0,0,0);font-family:Arial,Helvetica,sans-serif;font-size:12.8px"><font
              size="2" color="#000000"><i><font face="arial, helvetica,
                  sans-serif" color="#000000">Best Regards</font></i></font></i></div>
        <div>
          <div dir="ltr" class="gmail_signature"
            data-smartmail="gmail_signature">
            <div dir="ltr">
              <div>
                <div dir="ltr">
                  <div dir="ltr">
                    <div dir="ltr">
                      <div dir="ltr">
                        <div dir="ltr">
                          <div dir="ltr">
                            <div dir="ltr">
                              <div dir="ltr">
                                <div dir="ltr">
                                  <div dir="ltr">
                                    <div dir="ltr">
                                      <div dir="ltr">
                                        <div dir="ltr">
                                          <div dir="ltr">
                                            <div dir="ltr">
                                              <div dir="ltr">
                                                <div
                                                  style="color:rgb(0,0,0)"><i><font
                                                      size="2"
                                                      face="arial,
                                                      helvetica,
                                                      sans-serif">Saeid
                                                      Mohammadzadeh
                                                      Bina, Dr. (Eng.)</font></i></div>
                                                <div
                                                  style="color:rgb(0,0,0)"><i
style="font-size:12.8px;color:rgb(34,34,34)"><font size="2" face="times
                                                      new roman, new
                                                      york, times,
                                                      serif"
                                                      color="#000000"><i><font
                                                          size="3"
                                                          face="arial,
                                                          helvetica,
                                                          sans-serif"
                                                          color="#000000">-------------------------------------------------</font></i></font></i></div>
                                                <div
                                                  style="color:rgb(0,0,0);font-family:HelveticaNeue,"Helvetica
Neue",Helvetica,Arial,"Lucida Grande",sans-serif"><font
                                                    size="2" face="times
                                                    new roman, new york,
                                                    times, serif"
                                                    color="#000000">
                                                    <div align="left"><font
style="font-size:16px" size="3" face="arial, helvetica, sans-serif"><font
                                                          size="2"
                                                          face="times
                                                          new roman, new
                                                          york, times,
                                                          serif"
                                                          color="#000000">
                                                          <div
                                                          align="left"><em><font
                                                          face="times
                                                          new
                                                          roman,serif">Akita
                                                          <var></var>University</font></em><br>
                                                          </div>
                                                        </font></font><font
                                                        face="arial,
                                                        helvetica,
                                                        sans-serif"><font
                                                          size="2"
                                                          face="times
                                                          new roman, new
                                                          york, times,
                                                          serif"
                                                          color="#000000">
                                                          <div
                                                          align="left"><span
style="font-family:"Times New Roman",serif"><i>Graduate
                                                          school of
                                                          International
                                                          Resource
                                                          Sciences</i></span><font
                                                          face="times
                                                          new
                                                          roman,serif"><em>.<br>
                                                          1-1 Tegata
                                                          gakuen-machi,
                                                          Akita
                                                          010-8502,
                                                          Japan</em></font></div>
                                                          <div
                                                          align="left"><font
                                                          face="times
                                                          new
                                                          roman,serif"><em>Tel: </em></font><em
style="font-family:"times new roman",serif">+815068665026
                                                          (Japan)</em></div>
                                                          <div
                                                          align="left"><em
style="font-family:"times new roman",serif">     
                                                           +989141011757
                                                          (Iran)</em><em
style="font-family:"times new roman",serif">   </em></div>
                                                        </font></font></div>
                                                    <div align="left"><font
style="font-size:16px" size="3" face="garamond, new york, times, serif"><em>E-mail: </em></font><a
href="mailto:s.mohammadzadeh66@gmail.com" target="_blank"
                                                        moz-do-not-send="true"><em>d9515254@s.akita-u.ac.jp</em></a><em
style="font-size:16px"> </em></div>
                                                    <div
                                                      style="font-size:16px"
                                                      align="left"><em
                                                        style="font-family:garamond,"new
york",times,serif;font-size:medium;background-color:rgba(0,0,0,0);margin:0px;padding:0px;color:blue"> 
                                                                 <a
                                                          href="mailto:mohammadzadehsaeid@yahoo.com"
                                                          rel="nofollow"
style="font-family:garamond,"new
york",times,serif;font-size:medium;background-color:rgba(0,0,0,0);margin:0px;padding:0px;color:blue"
target="_blank" moz-do-not-send="true">mohammadzadehsaeid@yahoo.com</a></em></div>
                                                  </font><font
                                                    style="font-size:16px"
                                                    size="2" face="times
                                                    new roman, new york,
                                                    times, serif"
                                                    color="#000000">
                                                    <div align="left">
                                                      <div
                                                        style="font-family:HelveticaNeue,"Helvetica
Neue",Helvetica,Arial,"Lucida
                                                        Grande",sans-serif;font-size:16px"><i><font
                                                          size="2"
                                                          face="times
                                                          new roman, new
                                                          york, times,
                                                          serif"
                                                          color="#000000"><i><font
                                                          size="3"
                                                          face="arial,
                                                          helvetica,
                                                          sans-serif"
                                                          color="#000000">-------------------------------------------------<br>
                                                          <br>
                                                          </font></i></font></i></div>
                                                    </div>
                                                  </font></div>
                                              </div>
                                            </div>
                                          </div>
                                        </div>
                                      </div>
                                    </div>
                                  </div>
                                </div>
                              </div>
                            </div>
                          </div>
                        </div>
                      </div>
                    </div>
                  </div>
                </div>
              </div>
            </div>
          </div>
        </div>
        <br>
      </div>
      <br>
      <div class="gmail_quote">
        <div dir="ltr" class="gmail_attr">On Thu, Aug 13, 2020 at 11:32
          PM David BRADLEY <<a href="mailto:d.bradley@tess-inc.com"
            moz-do-not-send="true">d.bradley@tess-inc.com</a>> wrote:<br>
        </div>
        <blockquote class="gmail_quote" style="margin:0px 0px 0px
          0.8ex;border-left:1px solid rgb(204,204,204);padding-left:1ex">
          <div>
            <p>Dr Bina,</p>
            <p>  If you have access to the TESS Applications Library,
              you can define such schedules using the Types in that
              library. In TRNBuild you will need to select that the
              schedule values will come from INPUTS instead of from
              SCHEDULES that are defined inside TRNBuild.</p>
            <p>best,</p>
            <p> David</p>
            <p><br>
            </p>
            <div>On 08/12/2020 23:12, saeid mohammadzadeh via
              TRNSYS-users wrote:<br>
            </div>
            <blockquote type="cite">
              <div dir="ltr">
                <div class="gmail_default"
                  style="font-family:arial,helvetica,sans-serif;font-size:small">Hello
                  dear TRNSYS users;</div>
                <div class="gmail_default"
                  style="font-family:arial,helvetica,sans-serif;font-size:small"><br>
                </div>
                <div class="gmail_default"
                  style="font-family:arial,helvetica,sans-serif;font-size:small">I
                  have a question regarding the schedule for heating and
                  cooling:</div>
                <div class="gmail_default"
                  style="font-family:arial,helvetica,sans-serif;font-size:small">Firstly,
                  I want to calculate the heating and cooling loads
                  using the energy balance method (just on the heating
                  the cooling buttons) based on the following time
                  table:</div>
                <div class="gmail_default"
                  style="font-family:arial,helvetica,sans-serif;font-size:small">For
                  weekdays from 8 to 18 (either cooling or heating);</div>
                <div class="gmail_default"
                  style="font-family:arial,helvetica,sans-serif;font-size:small">For
                  the weekends off (either cooling or heating);</div>
                <div class="gmail_default"
                  style="font-family:arial,helvetica,sans-serif;font-size:small">From
                  Nov. to April "Heating"; </div>
                <div class="gmail_default"
                  style="font-family:arial,helvetica,sans-serif;font-size:small">From
                  Jul. to Sep. "Cooling".</div>
                <div class="gmail_default"
                  style="font-family:arial,helvetica,sans-serif;font-size:small">Secondly,
                  I would like to use this schedule and also
                  thermostat (either schedule or zone temperature is 1
                  for heating or cooling) to command the airconditioning
                  system that I will add later. </div>
                <div class="gmail_default"
                  style="font-family:arial,helvetica,sans-serif;font-size:small"><br>
                </div>
                <div class="gmail_default"
                  style="font-family:arial,helvetica,sans-serif;font-size:small">And
                  another issue, which is not important now, on weekdays
                  later I want to use complex timing (8 to 18 full
                  occupancy and other hours ratio of office workers). </div>
                <div class="gmail_default"
                  style="font-family:arial,helvetica,sans-serif;font-size:small"><br>
                </div>
                <div>
                  <div dir="ltr">
                    <div dir="ltr">
                      <div>
                        <div dir="ltr">
                          <div dir="ltr">
                            <div dir="ltr">
                              <div dir="ltr">
                                <div dir="ltr">
                                  <div dir="ltr">
                                    <div dir="ltr">
                                      <div dir="ltr">
                                        <div dir="ltr">
                                          <div dir="ltr">
                                            <div dir="ltr">
                                              <div dir="ltr">
                                                <div dir="ltr">
                                                  <div dir="ltr">
                                                    <div dir="ltr">
                                                      <div dir="ltr">
                                                        <div
                                                          style="color:rgb(0,0,0)"><i
style="font-size:12.8px"><font size="2" color="#000000"><i><font
                                                          face="arial,
                                                          helvetica,
                                                          sans-serif"
                                                          color="#000000">Best
                                                          Regards</font></i></font></i><br>
                                                        </div>
                                                        <div
                                                          style="color:rgb(0,0,0)"><i><font
                                                          size="2"
                                                          face="arial,
                                                          helvetica,
                                                          sans-serif">Saeid
                                                          Mohammadzadeh
                                                          Bina, Dr.
                                                          (Eng.)</font></i></div>
                                                        <div
                                                          style="color:rgb(0,0,0)"><i
style="font-size:12.8px;color:rgb(34,34,34)"><font size="2" face="times
                                                          new roman, new
                                                          york, times,
                                                          serif"
                                                          color="#000000"><i><font
                                                          size="3"
                                                          face="arial,
                                                          helvetica,
                                                          sans-serif"
                                                          color="#000000">-------------------------------------------------</font></i></font></i></div>
                                                        <div><font
                                                          size="2"
                                                          face="times
                                                          new roman, new
                                                          york, times,
                                                          serif"
                                                          color="#000000">
                                                          <div
                                                          align="left"><font
style="font-size:16px" size="3" face="arial, helvetica, sans-serif"><font
                                                          size="2"
                                                          face="times
                                                          new roman, new
                                                          york, times,
                                                          serif"
                                                          color="#000000">
                                                          <div
                                                          align="left"><em><font
                                                          face="times
                                                          new
                                                          roman,serif">Akita
                                                          <var></var>University</font></em><br>
                                                          </div>
                                                          </font></font><font
                                                          face="arial,
                                                          helvetica,
                                                          sans-serif"><font
                                                          size="2"
                                                          face="times
                                                          new roman, new
                                                          york, times,
                                                          serif"
                                                          color="#000000">
                                                          <div
                                                          align="left"><span
style="font-family:"Times New Roman",serif"><i>Graduate school
                                                          of
                                                          International
                                                          Resource
                                                          Sciences</i></span><font
                                                          face="times
                                                          new
                                                          roman,serif"><em>.<br>
                                                          1-1 Tegata
                                                          gakuen-machi,
                                                          Akita
                                                          010-8502,
                                                          Japan</em></font></div>
                                                          <div
                                                          align="left"><font
                                                          face="times
                                                          new
                                                          roman,serif"><em>Tel: </em></font><em
style="font-family:"times new roman",serif">+815068665026
                                                          (Japan)</em></div>
                                                          <div
                                                          align="left"><em
style="font-family:"times new roman",serif">     
                                                           +989141011757
                                                          (Iran)</em><em
style="font-family:"times new roman",serif">   </em></div>
                                                          </font></font></div>
                                                          <div
                                                          align="left"><font
style="font-size:16px" size="3" face="garamond, new york, times, serif"><em>E-mail: </em></font><a
href="mailto:s.mohammadzadeh66@gmail.com" target="_blank"
                                                          moz-do-not-send="true"><em>d9515254@s.akita-u.ac.jp</em></a><em
style="font-size:16px"> </em></div>
                                                          <div
                                                          style="font-size:16px"
                                                          align="left"><em> 
                                                                   <a
                                                          href="mailto:mohammadzadehsaeid@yahoo.com"
                                                          rel="nofollow"
target="_blank" moz-do-not-send="true">mohammadzadehsaeid@yahoo.com</a></em></div>
                                                          </font><font
                                                          style="font-size:16px"
                                                          size="2"
                                                          face="times
                                                          new roman, new
                                                          york, times,
                                                          serif"
                                                          color="#000000">
                                                          <div
                                                          align="left">
                                                          <div><i><font
                                                          size="2"
                                                          face="times
                                                          new roman, new
                                                          york, times,
                                                          serif"
                                                          color="#000000"><i><font
                                                          size="3"
                                                          face="arial,
                                                          helvetica,
                                                          sans-serif"
                                                          color="#000000">-------------------------------------------------<br>
                                                          <br>
                                                          </font></i></font></i></div>
                                                          </div>
                                                          </font></div>
                                                      </div>
                                                    </div>
                                                  </div>
                                                </div>
                                              </div>
                                            </div>
                                          </div>
                                        </div>
                                      </div>
                                    </div>
                                  </div>
                                </div>
                              </div>
                            </div>
                          </div>
                        </div>
                      </div>
                    </div>
                  </div>
                </div>
              </div>
              <br>
              <fieldset></fieldset>
              <pre>_______________________________________________
TRNSYS-users mailing list
<a href="mailto:TRNSYS-users@lists.onebuilding.org" target="_blank" moz-do-not-send="true">TRNSYS-users@lists.onebuilding.org</a>
<a href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org" target="_blank" moz-do-not-send="true">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
            </blockquote>
            <pre cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a href="mailto:d.bradley@tess-inc.com" target="_blank" moz-do-not-send="true">d.bradley@tess-inc.com</a>

<a href="http://www.tess-inc.com" target="_blank" moz-do-not-send="true">http://www.tess-inc.com</a>
<a href="http://www.trnsys.com" target="_blank" moz-do-not-send="true">http://www.trnsys.com</a></pre>
          </div>
        </blockquote>
      </div>
    </blockquote>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>