[TRNSYS-users] Issue in auxiliary operations with Type941 (Heat Pump from TESS)
David BRADLEY
d.bradley at tess-inc.com
Mon Oct 28 07:33:47 PDT 2019
Thank you for pointing this out Antoine. We will certainly get it fixed.
kind regards,
David
On 10/28/2019 04:59, LECONTE Antoine 219492 via TRNSYS-users wrote:
>
> I have noticed a potential issue with the use of the auxiliary system
> of the Heat Pump Type 941 (from TESS library).
>
> In the source code (Type941.for), there is no value setting for QAUX
> when all signals à “OFF”.
>
> This means that an auxiliary consumption can be computed whereas its
> operation mode is “OFF”.
>
> For instance : in one time step you have “Heating mode “ and “Aux
> mode” both “ON”; if in the next timestep all signals are “OFF”, Type
> 941 will still set QAUX > 0 as an output.
>
> This can be easily fixed by either adding an additional condition on
> the calculation of QAUX directly in the TRNSYS model or by
> re-compiling type 941 with an additional “QAUX=0.” In the “NO-FLOW
> CONDITIONS”.
>
> Best regards,
>
> ------------------------------------------------------------------------------------------
>
> Description : cid:image001.png at 01CF110C.81BE0EF0
>
>
>
> *Antoine LECONTE***
>
> *Research Engineer*
>
> /National Institute of Solar Energy /
>
> *CEA/LITEN - Department of Solar Energy***
>
> *Building and Thermal Systems*
>
> Description : cid:image002.jpg at 01CF110C.81BE0EF0**
>
> Commissariat à l’énergie atomique et aux énergies alternatives
>
> Bât. HELIOS, 50 avenue du Lac Léman *|*F-73375 Le Bourget-du-Lac
>
> T. +33 (0)4 79 79 21 38 *|*F. +33 (0) 4 79 62 13 74 *|*
>
> antoine.leconte at cea.fr <mailto:antoine.leconte at cea.fr>;
> www.ines-solaire.org <http://www.ines-solaire.org/>; liten.cea.fr
>
> ------------------------------------------------------------------------------------------
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20191028/775871dd/attachment-0001.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 10820 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20191028/775871dd/attachment-0001.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 1321 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20191028/775871dd/attachment-0001.jpg>
More information about the TRNSYS-users
mailing list