[TRNSYS-users] Thermal storage tank
    ARRATE HERNANDEZ 
    arrate.hernandez at ehu.eus
       
    Fri Mar  8 05:36:17 PST 2019
    
    
  
Thanks,
Arrate
Jeff Thornton via TRNSYS-users <trnsys-users at lists.onebuilding.org> escribió:
> 534 requires that you have matched inlets and outlets but it’s easy  
> to mimic un-matched ports by using a simple mixing valve.  If you  
> have three inlets and two outlets in reality, you just set it up as  
> 3 and 3 in 534 and mix the two together that are leaving from the  
> same location,
>
> Jeff
>
> Sent from my iPhone
>
>> On Mar 7, 2019, at 4:51 AM, Hamidreza Esfehani via TRNSYS-users  
>> <trnsys-users at lists.onebuilding.org> wrote:
>>
>> You can define different number of inlet and outlets ports which I  
>> think is what you are looking for.
>>
>> -----Ursprüngliche Nachricht-----
>> Von: TRNSYS-users  
>> [mailto:trnsys-users-bounces at lists.onebuilding.org] Im Auftrag von  
>> ARRATE HERNANDEZ via TRNSYS-users
>> Gesendet: Donnerstag, 7. März 2019 11:29
>> An: TRNSYS users mailing list at OneBuilding.org  
>> <trnsys-users at lists.onebuilding.org>
>> Cc: ARRATE HERNANDEZ <arrate.hernandez at ehu.eus>
>> Betreff: Re: [TRNSYS-users] Thermal storage tank
>>
>> Thanks a million. And is there any type that allows to define  
>> different number of inputs and outputs?
>>
>> Hamidreza Esfehani via TRNSYS-users
>> <trnsys-users at lists.onebuilding.org> escribió:
>>
>>> Dear Arrate,
>>>
>>> you can use Type 534 from Storage Tank Library (TESS).
>>> There you can give the number of ports (paired input/output) that you need.
>>>
>>> Best,
>>> Hamid
>>>
>>> Hamidreza Heidar Esfehani
>>> Wissenschaftlicher Mitarbeiter|Research Associate
>>>
>>> Leibniz Universität Hannover
>>> IEK Abt.Gebäudetechnik
>>> Herrenhäuser Str. 8
>>> 30419 Hannover
>>>
>>> Telefon : +49 (0)511 762 3811
>>> Fax : +49 (0)511 762 3016
>>> hamidreza.esfehani at iek.uni-hannover.de
>>>
>>> www.iek.uni-hannover.de/gebaeudetechnik
>>> -----Ursprüngliche Nachricht-----
>>> Von: TRNSYS-users [mailto:trnsys-users-bounces at lists.onebuilding.org]
>>> Im Auftrag von ARRATE HERNANDEZ via TRNSYS-users
>>> Gesendet: Donnerstag, 7. März 2019 11:14
>>> An: trnsys-users at lists.onebuilding.org
>>> Cc: ARRATE HERNANDEZ <arrate.hernandez at ehu.eus>
>>> Betreff: [TRNSYS-users] Thermal storage tank
>>>
>>> Dear users,
>>>
>>> I need a stratified cylinder storage tank with 3 inputs and 2 outputs
>>> to my project. Any of you know how can I get it? Thanks,
>>>
>>> Arrate
>>>
>>>
>>> _______________________________________________
>>> TRNSYS-users mailing list
>>> TRNSYS-users at lists.onebuilding.org
>>> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
>>>
>>> _______________________________________________
>>> TRNSYS-users mailing list
>>> TRNSYS-users at lists.onebuilding.org
>>> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
>>
>>
>>
>> _______________________________________________
>> TRNSYS-users mailing list
>> TRNSYS-users at lists.onebuilding.org
>> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
>>
>> _______________________________________________
>> TRNSYS-users mailing list
>> TRNSYS-users at lists.onebuilding.org
>> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
    
    
More information about the TRNSYS-users
mailing list