[TRNSYS-users] Thermal storage tank

Jeff Thornton thornton at tess-inc.com
Thu Mar 7 07:02:17 PST 2019


534 requires that you have matched inlets and outlets but it’s easy to mimic un-matched ports by using a simple mixing valve.  If you have three inlets and two outlets in reality, you just set it up as 3 and 3 in 534 and mix the two together that are leaving from the same location,

Jeff 

Sent from my iPhone

> On Mar 7, 2019, at 4:51 AM, Hamidreza Esfehani via TRNSYS-users <trnsys-users at lists.onebuilding.org> wrote:
> 
> You can define different number of inlet and outlets ports which I think is what you are looking for.
> 
> -----Ursprüngliche Nachricht-----
> Von: TRNSYS-users [mailto:trnsys-users-bounces at lists.onebuilding.org] Im Auftrag von ARRATE HERNANDEZ via TRNSYS-users
> Gesendet: Donnerstag, 7. März 2019 11:29
> An: TRNSYS users mailing list at OneBuilding.org <trnsys-users at lists.onebuilding.org>
> Cc: ARRATE HERNANDEZ <arrate.hernandez at ehu.eus>
> Betreff: Re: [TRNSYS-users] Thermal storage tank
> 
> Thanks a million. And is there any type that allows to define different number of inputs and outputs?
> 
> Hamidreza Esfehani via TRNSYS-users
> <trnsys-users at lists.onebuilding.org> escribió:
> 
>> Dear Arrate,
>> 
>> you can use Type 534 from Storage Tank Library (TESS).
>> There you can give the number of ports (paired input/output) that you need.
>> 
>> Best,
>> Hamid
>> 
>> Hamidreza Heidar Esfehani
>> Wissenschaftlicher Mitarbeiter|Research Associate
>> 
>> Leibniz Universität Hannover
>> IEK Abt.Gebäudetechnik
>> Herrenhäuser Str. 8
>> 30419 Hannover
>> 
>> Telefon : +49 (0)511 762 3811
>> Fax : +49 (0)511 762 3016
>> hamidreza.esfehani at iek.uni-hannover.de
>> 
>> www.iek.uni-hannover.de/gebaeudetechnik
>> -----Ursprüngliche Nachricht-----
>> Von: TRNSYS-users [mailto:trnsys-users-bounces at lists.onebuilding.org] 
>> Im Auftrag von ARRATE HERNANDEZ via TRNSYS-users
>> Gesendet: Donnerstag, 7. März 2019 11:14
>> An: trnsys-users at lists.onebuilding.org
>> Cc: ARRATE HERNANDEZ <arrate.hernandez at ehu.eus>
>> Betreff: [TRNSYS-users] Thermal storage tank
>> 
>> Dear users,
>> 
>> I need a stratified cylinder storage tank with 3 inputs and 2 outputs 
>> to my project. Any of you know how can I get it? Thanks,
>> 
>> Arrate
>> 
>> 
>> _______________________________________________
>> TRNSYS-users mailing list
>> TRNSYS-users at lists.onebuilding.org
>> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
>> 
>> _______________________________________________
>> TRNSYS-users mailing list
>> TRNSYS-users at lists.onebuilding.org
>> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
> 
> 
> 
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
> 
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org



More information about the TRNSYS-users mailing list