[TRNSYS-users] Type 123 Cooling Coil Psychometrics Problem
Hofmann, Daniel
daniel.hofmann at dreso.com
Wed Jul 17 04:13:56 PDT 2019
Hello David,
I jumped over to a sensible heat exchanger. This solution works perfectly for me.
Many thanks for your help and the description of the problem
best regards,
Daniel Hofmann
From: David BRADLEY <d.bradley at tess-inc.com>
Sent: Tuesday, July 16, 2019 9:47 PM
To: TRNSYS users mailing list at OneBuilding.org <trnsys-users at lists.onebuilding.org>
Cc: Hofmann, Daniel <daniel.hofmann at dreso.com>
Subject: Re: [TRNSYS-users] Type 123 Cooling Coil Psychometrics Problem
Daniel,
Type123 does a computation to find the maximum possible heat transfer at the given rated conditions (air and water inlet temperature, air inlet humidity, air and water flow rates). It then compares the stated capacity to the calculated maximum. In the case of the parameters that you have specified below, the maximum possible heat transfer is being calculated as 234. kJ/h. However! if you reduce the total and sensible heat transfer rates to that value you will run into another error.
Fundamentally, the problem is that while Type123 assumes that the coil is either totally dry or totally wet during operation its basic UA calculation method is invalid if the coil's rated conditions are for sensible-only heat transfer. We will certainly work on making some better error handling for Type123. I think the workaround for your case would be one of two things. You can either give the model some rated conditions in which the total capacity is greater than the sensible capacity or you could simply use a sensible-only heat exchanger model for your cooling coil.
kind regards,
David
On 07/16/2019 06:19, Hofmann, Daniel via TRNSYS-users wrote:
Hello everyone,
I currently try to use Type 123 Cooling Coil with TRNSYS18. Type 123 is directly connected to the TRY2017 weather data reader. All other inputs to Type 123 are considered to be constant.
The rated parameter values are measured values and do not include any dehumidification.
[cid:image001.jpg at 01D53CA1.25AC0790]
No matter whether I use humidity mode 1 or 2 and no matter whether I reduce the total cooling capacity to e.g. 400 kJ/hr I always get the following error: "The referenced Unit has a bad parameter value. Reported information: Parameter #7, Reported Problem: The total cooling capacity of the coil is impossible at the given conditions."
And an additional warning message is shown: "The referenced Unit has called the PSYCHOMETRICS routine one or more times during the simulation with a humidity ratio above the saturation humidity ratio for the given dry bulb temperature. The air was assumed saturated at the given dry bulb temperature and the humidity ratio set for this condition."
I already checked the connection between the weather data reader and Type 123. I also tried a simulation with constant input values.....there is still not difference.
Thus I think it is a bug in Type 123 or the psych subroutine.
Does anyone have a solution or an idea what could cause the errors? Thanks a lot for any help!
Best regards
Daniel Hofmann
_______________________________________________
TRNSYS-users mailing list
TRNSYS-users at lists.onebuilding.org<mailto:TRNSYS-users at lists.onebuilding.org>
http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com<mailto:d.bradley at tess-inc.com>
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20190717/37fb4049/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 34025 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20190717/37fb4049/attachment-0002.jpg>
More information about the TRNSYS-users
mailing list