[TRNSYS-users] simulate big amount of stuff inside industrail building
David BRADLEY
d.bradley at tess-inc.com
Mon Jan 21 14:47:30 PST 2019
There are two possibilities. The first is to compute the thermal mass of
the stuff and set that value as the thermal capacitance of the Type56
zone (I assume you are using Type56). This option assumes that the air
of the zone and the stuff in the zone are always at the same
temperature. If that is not a good assumption and you want to
characterize the air and the stuff as having different temperatures then
you might look at the TESS Loads and Structures library where you will
find a lumped capacitance model. Again, you'd compute the thermal mass
of the stuff in the zone and set the lumped capacitance accordingly.
However, the lump and the zone would then impact each other by means of
the temperature of the space (passed from 56 to the lump) and convective
and radiative energy gains (passed from the lump back to Type56).
kind regards,
David
On 01/21/2019 07:43, Mauro Cannistraro via TRNSYS-users wrote:
> Hi all, i wondering how to simulate a big amount of stuff ( great
> mass, great thermal inertia) inside an industrial building?
>
> tks in advance.
>
> *Ing. Phd. Mauro Cannistraro*
>
> **/University of Ferrara - Department of Architecture/
>
> /TekneHub. Via Saragat 13 - 44122 Ferrara (I)/
>
> /Tel. +39 0532 29 3662//
> /
>
> /Mob. +39 329 97 40 211/
>
> /Mail. mauro.cannistraro at unife.it <mailto:mauro.cannistraro at unife.it>/
>
> /Pec. mauro.cannistraro at ordineingpa.it
> <mailto:mauro.cannistraro at ordineingpa.it> /
>
>
> Le informazioni trasmesse sono destinate esclusivamente alla persona o
> alla società in indirizzo e sono da intendersi confidenziali e
> riservate. Ogni trasmissione, inoltro, diffusione o altro uso di
> queste informazioni a persone o società differenti dal destinatario è
> proibita
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com