[TRNSYS-users] Output - latent cooling load of type 56
David BRADLEY
d.bradley at tess-inc.com
Sat Feb 2 06:24:43 PST 2019
Maria,
A latent cooling load is the latent energy that has to be removed from
or added to the air in order to maintain a humidity set point. So unless
you define a humidity setpoint, there will not be a latent load.
That said, often the way buildings are cooled causes there to be some
latent energy removal from the space while performing sensible cooling
to maintain space set point temperatures. There is a component in the
TESS Loads and Structures library (Type2280 - latent load calculator)
that makes an estimate of the amount of latent energy removal that
happens as a result of sensible cooling. If you have access to that
library, I would recommend using that component.
kind regards,
David
On 01/31/2019 20:13, Maria Panagiotidou via TRNSYS-users wrote:
> Dear users,
>
> I am calculating the heating and cooling load of a residential
> building. I have an unlimited heating and an unlimited cooling system
> (without humidification/dehumidification). I can't find the output (of
> Type 56) for the latent cooling load. I can see the output of latent
> gains, the humidification/dehumidification cooling load, but I don't
> see anything for the latent cooling load without
> humidification/dehumidification.
> Could anybody help me?
>
> Kind Regards,
> Maria Panagiotidou
> PhD candidate
> The University of Melbourne
> Victoria
> 3010 Australia
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20190202/3fbc5a16/attachment.html>
More information about the TRNSYS-users
mailing list