    <p>Maria,</p>
    <p> A latent cooling load is the latent energy that has to be
      removed from or added to the air in order to maintain a humidity
      set point. So unless you define a humidity setpoint, there will
      not be a latent load. <br>
    </p>
    <p>  That said, often the way buildings are cooled causes there to
      be some latent energy removal from the space while performing
      sensible cooling to maintain space set point temperatures. There
      is a component in the TESS Loads and Structures library (Type2280
      - latent load calculator) that makes an estimate of the amount of
      latent energy removal that happens as a result of sensible
      cooling. If you have access to that library, I would recommend
      using that component.</p>
    <p>kind regards,</p>
    <p> David</p>
    <p><br>
    </p>
    <div class="moz-cite-prefix">On 01/31/2019 20:13, Maria Panagiotidou
      via TRNSYS-users wrote:<br>
    </div>
    <blockquote type="cite"
cite="mid:CAFpY=Piw8GBkrx5cF2WsNXB5a0O2gvAidExA6mVZzKggTE5Psg@mail.gmail.com">
      <meta http-equiv="content-type" content="text/html; charset=UTF-8">
      <div dir="ltr">Dear users,
        <div><br>
        </div>
        <div>I am calculating the heating and cooling load of a
          residential building. I have an unlimited heating and an
          unlimited cooling system (without
          humidification/dehumidification). I can't find the output (of
          Type 56) for the latent cooling load. I can see the output of
          latent gains, the humidification/dehumidification cooling
          load, but I don't see anything for the latent cooling load
          without 
          humidification/dehumidification. </div>
        <div>Could anybody help me?</div>
        <div><br>
        </div>
        <div>Kind Regards, <br clear="all">
          <div>
            <div dir="ltr" class="gmail_signature"
              data-smartmail="gmail_signature">
              <div dir="ltr">
                <div dir="ltr">Maria Panagiotidou
                  <div>PhD candidate</div>
                  <div><font color="#666666"><span
                        style="background-color:rgb(255,255,255)"><span
                          style="font-family:sans-serif;font-size:13px">The
                          University of Melbourne </span></span></font></div>
                  <div><font color="#666666"><span
                        style="background-color:rgb(255,255,255)">Victoria<br
                          style="font-family:sans-serif;font-size:13px">
                        <span
                          style="font-family:sans-serif;font-size:13px">3010
                          Australia</span></span><br>
                    </font></div>
                  <div><br>
                  </div>
                </div>
              </div>
            </div>
          </div>
        </div>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <pre class="moz-quote-pre" wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
    </blockquote>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>