[TRNSYS-users] type 49 external files
David BRADLEY
d.bradley at tess-inc.com
Mon Dec 30 09:10:51 PST 2019
Emre,
The soil_temperatures file is created by Type49. It is not one that
you have to create. You can give it any name you want. The file will be
text and can be viewed using the GroundTempViewer.exe that is located in
the ..\TrnsysXX\Tools directory.
kind regards,
David
On 12/28/2019 12:29, Emre Arpaci via TRNSYS-users wrote:
> hi everyone happy new year to all.
> I have a problem about creating external files to type 49.
> i will use type 49 to determine the ground temperature of the my
> greenhouse. I read the TRNSYS Multizone Slab Model Tutorial and
> Example. I used the tess soilnoding plugin to create the files. I
> answered all questions by asked tess soilnoding. finally the program
> created two files but one is empty. my zoneXYDistances file is empty
> as you can see the figure . My zone_Soil Noding File is only 4 lines.
> is that normal ?
> And type49's external file is soil_temperatures(it is the second one
> external file) how can ı create this soil_temperatures file? or which
> file i have to use for the soil temperature ( type 49 external
> 2.file= final soil temperature profile)
> thanks
> image.png
> image.png
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20191230/dd8b5274/attachment-0001.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image.png
Type: image/png
Size: 151293 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20191230/dd8b5274/attachment-0002.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image.png
Type: image/png
Size: 145058 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20191230/dd8b5274/attachment-0003.png>
More information about the TRNSYS-users
mailing list