[TRNSYS-users] Complex fenestration model
Joaquim Romaní Picas
jromani at irec.cat
Wed Apr 3 07:02:54 PDT 2019
Dear all,
I am interested on using the "complex fenestration" add-on for TRNSYS18. I have found the mathematical description on the documentation, yet I have not found how to add a complex fenestration to my Type56. I would like to know which is the format needed to build the "construction" and "BSDF" data with WINDOW and how it is imported to TRNSYS.
Is there any information about it beyond the course "training 7: complex fenestration modelling with TRSNSY 18"?
Thanks in advance,
Joaquim
Joaquim Romaní
Researcher
Thermal Energy and Bulding Performance Group
+34 933 56 26 15 ext. 205
[cid:image003.jpg at 01D3A681.0D4A4700]
Institut de Rercerca en Energia de Catalunya
Catalonia Institute for Energy Research
www.irec.cat<http://www.irec.cat/>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20190403/c32ca211/attachment.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 4556 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20190403/c32ca211/attachment.jpg>
More information about the TRNSYS-users
mailing list