[TRNSYS-users] R: TRNBuild Cooling Load Calculations - Validation In Iran (Tehran)
Giuseppe Corallo
giuseppe.corallo at enea.it
Wed Sep 5 01:01:37 PDT 2018
Hi,
I just checked very quickly your .bui file: try to increase the
infiltration to at least 1 vol/h; extend the lights load to the entire
floor; include dehumidification with a relative humidity of about 50% and
calculate again.
Good luck
Giuseppe Corallo
Italy
Da: TRNSYS-users [mailto:trnsys-users-bounces at lists.onebuilding.org] Per
conto di Hooman Azad via TRNSYS-users
Inviato: domenica 2 settembre 2018 19:04
A: trnsys-users at lists.onebuilding.org
Cc: Hooman Azad
Oggetto: [TRNSYS-users] TRNBuild Cooling Load Calculations - Validation In
Iran (Tehran)
Dear Sir/Madam
Im trying to calculate the cooling load for a simple building located in
Tehran, Iran. The dimensions are 20m*10m*2.5m, with the 20m long façades
face due North-South, as you can see in the attached files. The Maximum
cooling load is obtained to be about 17000kJ/hr or 1.34 USRT which is about
0.007 USTR per square meter. In Iran, HVAC engineers use about 0.03 USRT per
square meter for Tehrans cooling load as a rule of thumb, which is about 4
times the result obtained from TRNBuild.
Please kindly help me with the issue, since TRNBuild is not used for
cooling/heating load calculations in Iran and Im trying to present it as a
useful tool. Your assistance could be very decisive.
Best Regards
Hooman Azad
Tehran
Iran