[TRNSYS-users] Convergence issue for stand-alone pv hydrogen system
David BRADLEY
d.bradley at tess-inc.com
Tue Oct 16 10:03:17 PDT 2018
Michel,
An hour time step is almost guaranteed not to work. Controllers can
make one decision per time step. That kind of frequency of decision
making can very easily lead to empty tanks, overcharged batteries etc.
You should be working with time steps between 1 and 5 minutes. Needing
multiple days to run TRNOpt optimizations is not uncommon at all.
The difference between the two solar plots would suggest that there
is some problem with the way the solar radiation data is being read and
processed. It would help to know what components you are using to read
and process the data and what version of Trnsys you are using.
kind regards,
David
On 10/12/2018 09:09, Michel Tamarzians via TRNSYS-users wrote:
> Dear,
>
> I am working on a simulation of a stand-alone pv-hydrogen-battery
> system. I am using the mastercontroller, "Unit 36", to control the
> power flow between the solar, battery, electrolyzer, fuel cell and
> load. Unfortunately when running the simulation for a whole year with
> timestep of 1 hour and the successive solver and differential equation
> algorithm of Heun or Euler it gives me convergence issues and stops
> the simulation. Ofcourse I can set the limit for the errors so high
> but then the simulation finishes with really strange results. For
> example even the solar energy coming in is totally changed throughout
> the year. If I make the timestep smaller, such as 0.01 then it works
> kinda oke but still the solar energy curve is totally different then
> it should be when nothing would be connected to it. See the two graphs
> added of the solar energy curve throughout the year.....
> Does anybody has a clue on how to tackle this convergence issue? Do I
> need to make the stepsize even smaller? But then it takes so long,
> that when I want to optimize my system with TRNOpt it takes probably
> about 3 days per simulation which is ridiculous by my understanding.
> Can someone please help me out or point me towards a direction on
> where to find a solution?
>
> Thanks in advance!
>
> Kind regards,
>
> Michel
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20181016/3adb5f5d/attachment.htm>
More information about the TRNSYS-users
mailing list