[TRNSYS-users] (no subject)

Jeff Thornton thornton at tess-inc.com
Mon May 7 20:50:47 PDT 2018


 

<How can i to specify (N_Sources * n_loads) data points> 

The data file takes a row of source temperatures and a row of load
temperatures. If there are 7 source and 6 load temperatures then you
will need to specify 42 lines of data. Please refer to the example data
files for the Type 668 model and the description of Type 42 - a
component that uses a similar data file structure and explains in great
detail how to set up the files. 

Jeff 

---
Jeff Thornton
President - TESS LLC
22 N. Carroll Street, Madison WI USA 53703
Office: (608) 274-2577 Fax: (608) 278-1475
www.tess-inc.com
E-Mail: thornton at tess-inc.com

On 05/07/2018 10:44 pm, berkane ahlem via TRNSYS-users wrote: 

> Hello sir
> How can i to specify (N_Sources * n_loads) data points
> I used heat pump type 668in trnsys 16 
> Thank you 
> 
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org [1]
 

Links:
------
[1]
http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20180507/9155f6a2/attachment.htm>


More information about the TRNSYS-users mailing list