[TRNSYS-users] TRNSYS type 60
David BRADLEY
d.bradley at tess-inc.com
Mon Mar 5 13:00:05 PST 2018
Mark,
If you have access to the TESS Storage library I would highly
recommend switching Type60 out for Type534. Type60 can get into some
numerically unstable regions from which it doesn't recover. In v18 we
dropped Type60 in favor of a few other tank models specifically because
of those problems.
kind regards,
David
On 03/05/2018 09:44, Zhiyong Tian via TRNSYS-users wrote:
>
> Hi,
>
> Does Anyone have experience with type 60 for storage tanks with
> internal heat exchangers?
>
> Im trying to model a system and have some problems with getting the
> tank to work properly.
>
> I want to have the temperatures of the notes/layers in the tank. Both
> to use for the control of the system and for comparing with
> measurement. I have made a project with only the type 60 to isolate
> the problem. When I run the simulation and I want to have the
> temperature of the layers it only gives me “0”.
>
> Hope to get some help, Thank you。
>
> Kind regards
>
> Mark Dannemand
>
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20180305/d075072b/attachment.htm>
More information about the TRNSYS-users
mailing list