Shiva,

  Adjacencies between rooms on the same level and adjacencies between 
floors are treated the same way in TRNBuild. There are two important 
pieces of information in this case:


1. the wall construction. This is a list of the layers that make up the 
wall and their respective thicknesses. The wall construction is given a 
name (such as OUTWALL, GROUND, INTFLOOR) but these are just names; they 
do not carry any information about where the walls are located in 
resepect to other walls in the building.

2. the wall category specifies how the wall is positioned. The choices 
are EXTERNAL (meaning that one side of the wall will receive solar 
radiation), ADJACENT (meaning that there are zones (airnodes) on both 
sides of the wall, BOUNDARY (which means that one side of the wall faces 
the zone and the other faces a known (and specified) boundary condition, 
and INTERNAL (which means that the wall is entirely contained inside a 
single zone.


kind regards,

  David



On 08/23/2018 03:53, Shiva Sharma via TRNSYS-users wrote:
>
> Hello guys,
>
>
> I am trying to build a building in Trnbuild with 2 floors. I am little 
> confuse about the surfaces and walls. Some of you might help me with 
> that. i checked restaurant example but its a single floor thus upper 
> ceiling is roof but how does it work when one wants to build 2 or more 
> floors. what option should i choose to make a ceiling between two 
> floors in wall type or there is other way. Should i choose INTFLOOR  
> or ROOF or Ground in wall type on Trnbuild? in category INTERNAL or 
> ADJACENT  ?
>
>
> Br,
>
> Shiva
>
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org

-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com

http://www.tess-inc.com
http://www.trnsys.com

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20180823/a2e2830c/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: pastedImage.png
Type: image/png
Size: 16008 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20180823/a2e2830c/attachment-0002.png>


More information about the TRNSYS-users mailing list