[TRNSYS-users] Turning ON-OFF Active system
David BRADLEY
d.bradley at tess-inc.com
Thu Aug 9 09:08:31 PDT 2018
Łukasz,
My apologies for the delay in responding; we've been moving offices
and so I have gotten behind.
Controlling the active layer with operative temperature is definitely
something that I have done. Set up the operative temperature as an
output of your Type56 model and then in the Studio, implement a
thermostat that watches the operative temperature and compares it to
your set point value. The thermostat model will then be connected to a
pump (and perhaps a boiler or a heat pump as well). Set the inlet
temperature and mass flow rate of liquid to your active layer as inputs
to Type56. In the Studio, the pump's output flow rate and temperature
will be the inputs to the Type56 active layer.
kind regards,
David
On 08/06/2018 08:17, Łukasz Wątły via TRNSYS-users wrote:
> Dear David,
>
> Thank you very much for your reply.
>
> However, I still would like to ask about one thing, since I am not
> much into this aspect. My goal is to control the flow rate of Active
> Layer (ceiling heating system) within the specified range of operative
> temperature. It means that I would like to switched off the active
> layer when the T_operative is higher than given value and then switch
> on again when the temperature drops below other value.
>
> Thus, I wonder how is it possible to change variables that are defined
> in TRNBuild (flow rate) in TRNSYS? Do you have any experience with that?
>
> Kind regards,
> Lukasz
>
>
> 2018-08-01 16:14 GMT+02:00 David BRADLEY <d.bradley at tess-inc.com
> <mailto:d.bradley at tess-inc.com>>:
>
> Łukasz,
>
> There aren't controls available within TRNBuild. Make the inlet
> temperature and flow rate to the active layer into inputs and then
> you can use whatever controls you like in the Studio to turn pumps
> and other devices on and off and thus control the temperature in
> the space. Make sure to use a short timestep (1-5 minutes) or the
> building will not stay reliably near its set points.
>
> kind regards,
>
> David
>
>
>
> On 07/31/2018 12:12, Łukasz Wątły via TRNSYS-users wrote:
>> Dear All,
>>
>> I am writing to you, since I would like to ask if there is a
>> possibility to control the Active Layer - radiant ceiling heating
>> system so that I could trigger it on\off whenever the airnode
>> temperature is below or above the certain limit? Is there an
>> option to do it in TRNBuild?
>>
>> I would be grateful for any guidance.
>>
>> Thanks in advance for your reply.
>>
>> Kind regards,
>> Lukasz Watly
>>
>>
>> _______________________________________________
>> TRNSYS-users mailing list
>> TRNSYS-users at lists.onebuilding.org
>> <mailto:TRNSYS-users at lists.onebuilding.org>
>> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
>> <http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org>
>
> --
> ***************************
> David BRADLEY
> Principal
> Thermal Energy Systems Specialists, LLC
> 22 North Carroll Street - suite 370
> Madison, WI 53703 USA
>
> P:+1.608.274.2577
> F:+1.608.278.1475
> d.bradley at tess-inc.com <mailto:d.bradley at tess-inc.com>
>
> http://www.tess-inc.com
> http://www.trnsys.com
>
>
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20180809/7696504c/attachment.htm>
More information about the TRNSYS-users
mailing list