[TRNSYS-users] Turning ON-OFF Active system

David BRADLEY d.bradley at tess-inc.com
Wed Aug 1 07:14:52 PDT 2018


Łukasz,

   There aren't controls available within TRNBuild. Make the inlet 
temperature and flow rate to the active layer into inputs and then you 
can use whatever controls you like in the Studio to turn pumps and other 
devices on and off and thus control the temperature in the space. Make 
sure to use a short timestep (1-5 minutes) or the building will not stay 
reliably near its set points.

kind regards,

  David



On 07/31/2018 12:12, Łukasz Wątły via TRNSYS-users wrote:
> Dear All,
>
> I am writing to you, since I would like to ask if there is a 
> possibility to control the Active Layer - radiant ceiling heating 
> system so that I could trigger it on\off whenever the airnode 
> temperature is below or above the certain limit? Is there an option to 
> do it in TRNBuild?
>
> I would be grateful for any guidance.
>
> Thanks in advance for your reply.
>
> Kind regards,
> Lukasz Watly
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org

-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com

http://www.tess-inc.com
http://www.trnsys.com

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20180801/32333adc/attachment.html>


More information about the TRNSYS-users mailing list