[TRNSYS-users] Question about type 56

Ale Vargas ale.varc93 at gmail.com
Wed Apr 25 09:37:01 PDT 2018


Thank you so much!

If I wanted to know the heat that radiant floor delivers to the house, I
would have to plot QALFL ?

Thanks in advance!

2018-04-25 13:21 GMT-03:00 hotline via TRNSYS-users <
trnsys-users at lists.onebuilding.org>:

> Dear Alejandra,
>
>
>
> QCOMI means energy from inside surf. incl. conv. to air and longwave
> radiation to other surfaces of one spec. surface while QSICONV only regards
> the inside energy gain by convection from air to spec. surface.
>
> B6_QCOMI is a balance output which is the same as QCOMI just for a
> complete zone.
>
> B6_QALG is total energy gains by an active layer or a chilled ceiling
> (heating -; cooling +) for a complete zone.
>
>
>
> QALE (If I use active layer): energy input by gains of active layer to
> active layer refers to the gain part in active layer.
>
> QALTL (If I use active layer): Is the sum of QALFL and QALE
>
>
>
> Best,
>
> Christoph
>
>
>
> *Von:* TRNSYS-users <trnsys-users-bounces at lists.onebuilding.org> *Im
> Auftrag von *Ale Vargas via TRNSYS-users
> *Gesendet:* Mittwoch, 25. April 2018 16:06
> *An:* trnsys-users at lists.onebuilding.org
> *Cc:* Ale Vargas <ale.varc93 at gmail.com>
> *Betreff:* [TRNSYS-users] Question about type 56
>
>
>
> Hello! I'm modelling a heating system composed by geothermal and solar
> energy, and this system delivers heat to the house through a radiant floor.
> I want to plot this heat (the heat that radiant floor delivers to the
> house).
>
>
>
> I was reading the outputs of type 56 in the documentation ("Multizone
> Building"), but I don´t understand this outputs and the diferences between
> them:
>
>
>
> QCOMI
>
> QSICONV
>
> B6_QCOMI
>
> B6_QALG
>
> QALE (If I use active layer)
>
> QALTL (If I use active layer)
>
>
>
> Can somebody explain me this outputs? Which of them could be suitable to
> plot the heat that radiant floor delivers to the house?
>
>
>
> Please, I need help!
>
> Thank you in advance!
>
>
>
> Alejandra.
>
>
> --
>
> *Alejandra Vargas Cáceres*
>
> *Estudiante Ingeniería Civil Mecánica*
>
> *Facultad de Ciencias Físicas y Matemáticas*
>
> *Universidad de Chile *
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
>
>


-- 

*Alejandra Vargas Cáceres*

*Estudiante Ingeniería Civil Mecánica*

*Facultad de Ciencias Físicas y Matemáticas*

*Universidad de Chile *
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20180425/e89d028f/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 8513 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20180425/e89d028f/attachment-0002.png>


More information about the TRNSYS-users mailing list