[TRNSYS-users] Type 954b - auxiliary efficiency

Jeff Thornton via TRNSYS-users trnsys-users at lists.onebuilding.org
Tue Sep 19 10:11:23 PDT 2017


 

Laura - you are correct. After checking the source code we have
discovered the problem. The auxiliary energy added to the air stream
does not include the impact of the auxiliary efficiency (simple typo).
It's an easy fix if you have a FORTRAN compiler and we'd be happy to
share it with you. Please let us know. Otherwise, we'll make the fix and
include it in the next release of the TESS HVAC Library. If you don't
have a compiler, there is still a somewhat easy work-around. Simply set
the capacity to the net capacity (capacity * efficiency) and set the
efficiency to one in the model. Then use an equation to calculate the
gross auxiliary input (auxiliary heat output from the model /
efficiency). 

Jeff 

---
Jeff Thornton
President - TESS LLC
22 N. Carroll Street, Madison WI USA 53703
Office: (608) 274-2577 Fax: (608) 278-1475
www.tess-inc.com
E-Mail: thornton at tess-inc.com

On 09/19/2017 11:36 am, Laura Guillon via TRNSYS-users wrote: 

> Hello everyone, 
> 
> I have an issue with the Type 954b (air source heat pump with a gas auxiliary system). 
> 
> I don't understand why the efficiency of the auxiliary heater is not totally taking into account by TRNSYS. 
> 
> Indeed, if I change the efficiency of the auxiliary system, I can see this change by plotting the output "total heat rate". However, regardless this change, the output temperature of the Type 954b remains the same. In other words, the output air temperature of the Type 954b does not seem influenced by the efficiency of the auxiliary system … 
> 
> To illustrate my issue, here is an example of data at one specific time (the capacity of the auxiliary system is 22,578 kJ/h) : 
> 
> Efficiency 
> 
> Total heat rate (output of the Type 954b) 
> 
> Input air temperature of the Type 954b 
> 
> Output air temperature of the Type 954b 
> 
> Airflow 
> 
> 90% 
> 
> 20,320 
> 
> 19.2 
> 
> 23.96 
> 
> 4,752 
> 
> 10% 
> 
> 2,258 
> 
> 19.2 
> 
> 23.96 
> 
> 4,752 
> 
> Is it normal ? Do you have an explanation to this ? 
> 
> If not, do you have any suggestions ? 
> 
> Thank you, 
> 
> Laura 
> 
>   
> 
> LAURA GUILLON, Jr. Eng M.A.Sc 
> 
> _Project Leader_ 
> 
> NATURAL GAS TECHNOLOGIES CENTRE 
> 
> 1350 Nobel, Suite 150, Boucherville, Quebec J4B 5H3 (Canada) 
> Tel.: 450-641-0021
> laura.guillon at ctgn.qc.ca 
> 
> www.ctgn.qc.ca [2] 
> 
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org [1]
 

Links:
------
[1]
http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
[2] http://www.ctgn.qc.ca/
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20170919/1dd33c39/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 11554 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20170919/1dd33c39/attachment-0002.jpg>


More information about the TRNSYS-users mailing list