Jakub,
As the author of Type997, I can tell you that the model most certainly
does NOT use 1/4 symmetry. There's no way to apply the symmetry as the
fluid changes temperature along the entire length axis and across the
entire width and depth of the piping array. That's why Type997 takes
both the left and right, and both the front and back, parameters
(insulation extension, far-field boundary etc.). If it was 1/4 symmetry
it would need only one of front/back or left/right. Why don't you send a
sketch showing what you'd like to model and we can see if 997 is the
right model. We have other more generic models that can handle a wider
range of geometries.
Jeff
---
Jeff Thornton
President - TESS LLC
22 N. Carroll Street, Madison WI USA 53703
Office: (608) 274-2577 Fax: (608) 278-1475
www.tess-inc.com
E-Mail: thornton at tess-inc.com
On 11/10/2017 4:15 am, Jakub Winiarski via TRNSYS-users wrote:
> Dear Users,
>
> Have anybody tried to modify the Type 997 component: Horizontal Field Ground Heat Exchanger, so that the insulation on Near Field surface can be set on just one side of HX domain? By deafult in order to reduce calculation cost the model is symmetrical in both x and y axis so that only quarter of domain is calculated. That is why the user can provide insulation on all four bounding surfaces or none. If there is a way to 'turn off' the symmetry in FORTRAN code and apply the boundary conditions on particular bounding surfaces it will be all I need.
> Perhaps someone already have done such modification?
>
> Best regards,
> JAKUB WINIARSKI
> R&D Specialist / Energy Simulations
>
> kom. +48 882 341 596
> e-mail: j.winiarski at mostostal.waw.pl
>
> mostostal.waw.pl
> BUDUJEMY PRZYSZŁOŚĆ.
> Mostostal Warszawa SA, ul. Konstruktorska 12A, 02-673 Warszawa, tel.: +48 22 250 70 00, fax: +48 22 250 70 01
> Sąd Rejonowy dla m. st. Warszawy w Warszawie, XIII Wydział Gospodarczy Krajowego Rejestru Sądowego
> Nr KRS 0000008820, NIP: 526-020-49-95, Regon: 012059053
>
> Jesteśmy jednym z sygnatariuszy Porozumienia dla Bezpieczeństwa w Budownictwie - inicjatywy utworzonej w sierpniu 2010 r. przez siedmiu największych generalnych wykonawców w naszym kraju. Misją Porozumienia jest prowadzenie działań na rzecz podniesienia poziomu kultury bezpieczeństwa pracy w branży budowlanej, a celem wyeliminowanie wypadków śmiertelnych na polskich budowach.
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org [1]
Links:
------
[1]
http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20171110/962d0215/attachment.html>
More information about the TRNSYS-users
mailing list