[TRNSYS-users] ODP: Re: [TRNSYS users] Type 997 modification (Horizontal Field Ground Heat Exchanger)
Jakub Winiarski
J.Winiarski at mostostal.waw.pl
Mon Nov 13 03:15:36 PST 2017
Jeff,
It's great to hear from the creator of the component! I have taken this
wrong assumption because the mathematical reference says that: "... For
the sake of simulation speed, the model breaks the ground along two axes
of symmetry (in the x and y directions) and simulates only one quarter of
the field, multiplying energy transfer results to arrive at the total
effect."
What I would like to simulate is something like:
38 pipes of 55m length in the ground buried on average 2.5m (centerline of
middle row). All pipes are connected at inlets and outlets with
collectors, and the same mass flow rate is assumed.
The HX is close to the building wall: 1.5m, which is insulated from the
outside. At the end I want also combine building thermal simulation with
the 997 type in simulation studio, but I dont' have building geometry yet.
The shift in the middle row can be neglected if the tool is not capable of
including that.
My goal is to simulate 25 years of HX and get outlet temperatures and
ground temperatures. I read that there's GroundTemperatureViewer tool
capable to see the .soil file, but it cannot find it yet.
Best regards,
Jakub Winiarski
R&D Specialist / Energy Simulations
kom. +48 882 341 596
e-mail: j.winiarski at mostostal.waw.pl
mostostal.waw.pl
BUDUJEMY PRZYSZŁOŚĆ.
Mostostal Warszawa SA, ul. Konstruktorska 12A, 02-673 Warszawa,
tel.: +48 22 250 70 00, fax: +48 22 250 70 01
Sąd Rejonowy dla m. st. Warszawy w Warszawie, XIII Wydział
Gospodarczy Krajowego Rejestru Sądowego
Nr KRS 0000008820, NIP: 526-020-49-95, Regon: 012059053
Jesteśmy jednym z sygnatariuszy Porozumienia dla Bezpieczeństwa w
Budownictwie – inicjatywy utworzonej w sierpniu 2010 r. przez siedmiu
największych generalnych wykonawców w naszym kraju. Misją Porozumienia
jest prowadzenie działań na rzecz podniesienia poziomu kultury
bezpieczeństwa pracy w branży budowlanej, a celem wyeliminowanie wypadków
śmiertelnych na polskich budowach.
Od: Jeff Thornton via TRNSYS-users
<trnsys-users at lists.onebuilding.org>
Do: "TRNSYS users mailing list at OneBuilding.org"
<trnsys-users at lists.onebuilding.org>
DW: Jeff Thornton <thornton at tess-inc.com>
Data: 10.11.2017 17:34
Temat: Re: [TRNSYS-users] [TRNSYS users] Type 997 modification
(Horizontal Field Ground Heat Exchanger)
Wysłane przez: "TRNSYS-users"
<trnsys-users-bounces at lists.onebuilding.org>
Jakub,
As the author of Type997, I can tell you that the model most certainly
does NOT use 1/4 symmetry. There's no way to apply the symmetry as the
fluid changes temperature along the entire length axis and across the
entire width and depth of the piping array. That's why Type997 takes both
the left and right, and both the front and back, parameters (insulation
extension, far-field boundary etc.). If it was 1/4 symmetry it would need
only one of front/back or left/right. Why don't you send a sketch showing
what you'd like to model and we can see if 997 is the right model. We
have other more generic models that can handle a wider range of
geometries.
Jeff
---
Jeff Thornton
President - TESS LLC
22 N. Carroll Street, Madison WI USA 53703
Office: (608) 274-2577 Fax: (608) 278-1475
www.tess-inc.com
E-Mail: thornton at tess-inc.com
On 11/10/2017 4:15 am, Jakub Winiarski via TRNSYS-users wrote:
Dear Users,
Have anybody tried to modify the Type 997 component: Horizontal Field
Ground Heat Exchanger, so that the insulation on Near Field surface can be
set on just one side of HX domain? By deafult in order to reduce
calculation cost the model is symmetrical in both x and y axis so that
only quarter of domain is calculated. That is why the user can provide
insulation on all four bounding surfaces or none. If there is a way to
'turn off' the symmetry in FORTRAN code and apply the boundary conditions
on particular bounding surfaces it will be all I need.
Perhaps someone already have done such modification?
Best regards,
Jakub Winiarski
R&D Specialist / Energy Simulations
kom. +48 882 341 596
e-mail: j.winiarski at mostostal.waw.pl
mostostal.waw.pl
BUDUJEMY PRZYSZŁOŚĆ.
Mostostal Warszawa SA, ul. Konstruktorska 12A, 02-673 Warszawa,
tel.: +48 22 250 70 00, fax: +48 22 250 70 01
Sąd Rejonowy dla m. st. Warszawy w Warszawie, XIII Wydział
Gospodarczy Krajowego Rejestru Sądowego
Nr KRS 0000008820, NIP: 526-020-49-95, Regon: 012059053
Jesteśmy jednym z sygnatariuszy Porozumienia dla Bezpieczeństwa w
Budownictwie – inicjatywy utworzonej w sierpniu 2010 r. przez siedmiu
największych generalnych wykonawców w naszym kraju. Misją Porozumienia
jest prowadzenie działań na rzecz podniesienia poziomu kultury
bezpieczeństwa pracy w branży budowlanej, a celem wyeliminowanie wypadków
śmiertelnych na polskich budowach.
_______________________________________________
TRNSYS-users mailing list
TRNSYS-users at lists.onebuilding.org
http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
_______________________________________________
TRNSYS-users mailing list
TRNSYS-users at lists.onebuilding.org
http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20171113/31990b5b/attachment-0001.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 10159 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20171113/31990b5b/attachment-0001.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 2734 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20171113/31990b5b/attachment-0002.jpe>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 2396 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20171113/31990b5b/attachment-0003.jpe>
More information about the TRNSYS-users
mailing list