[TRNSYS-users] TYPE 56, ADJ-WALL
    David BRADLEY via TRNSYS-users 
    trnsys-users at lists.onebuilding.org
       
    Mon Mar  6 07:06:28 PST 2017
    
    
  
In TRNBuild when you define an ADJACENT wall you'll note that the wall 
appears in two zones and that in the zone window there is a radio button 
with "front" and "back" options. If you open the wall manager you'll 
note that the materials are defined from "front" to "back" in the 
materials list. If you define a wall that has two layers (plaster and 
concrete) then note which material is listed first. This is the "front" 
of the wall. Go to the zone manager window and make sure that the 
appropriate zone contains the "front" of the wall. The wall thickness is 
not automatically doubled.
kind ergards,
  David
On 03/03/2017 09:09, Riccardo Nesa via TRNSYS-users wrote:
>
> HI TRNSYS USERS,
>
>
> In TRNBUILD if i have 2 adjacent rooms and i draw all the walls with 
> plaster and concrete (plaster is the interior surface, total thickness 
> of 20 cm),
>
>
> the ADJacent-WALL that separate the 2 rooms will be the sum of each 
> walls (so plaster-concrete-concrete-plaster, tickness=20+20=40 cm) or 
> will be the drawn wall (plaster-concrete, thickness=20cm)?
>
>
> THANK YOU
>
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20170306/252155d3/attachment-0003.htm>
    
    
More information about the TRNSYS-users
mailing list