    <p>In TRNBuild when you define an ADJACENT wall you'll note that the
      wall appears in two zones and that in the zone window there is a
      radio button with "front" and "back" options. If you open the wall
      manager you'll note that the materials are defined from "front" to
      "back" in the materials list. If you define a wall that has two
      layers (plaster and concrete) then note which material is listed
      first. This is the "front" of the wall. Go to the zone manager
      window and make sure that the appropriate zone contains the
      "front" of the wall. The wall thickness is not automatically
      doubled.</p>
    <p>kind ergards,</p>
    <p> David</p>
    <p><br>
    </p>
    <br>
    <div class="moz-cite-prefix">On 03/03/2017 09:09, Riccardo Nesa via
      TRNSYS-users wrote:<br>
    </div>
    <blockquote
cite="mid:VI1PR0602MB2959779848BA1BCEF0CF0ED48E2B0@VI1PR0602MB2959.eurprd06.prod.outlook.com"
      type="cite">
      <meta http-equiv="Content-Type" content="text/html;
        charset=windows-1252">
      <style type="text/css" style="display:none;"><!-- P {margin-top:0;margin-bottom:0;} --></style>
      <div id="divtagdefaultwrapper"
style="font-size:12pt;color:#000000;font-family:Calibri,Arial,Helvetica,sans-serif;"
        dir="ltr">
        <p>HI TRNSYS USERS,</p>
        <p><br>
        </p>
        <p>In TRNBUILD if i have 2 adjacent rooms and i draw all the
          walls with plaster and concrete (plaster is the interior
          surface, total thickness of 20 cm),</p>
        <p><br>
        </p>
        <p>the ADJacent-WALL that separate the 2 rooms will be the sum
          of each walls (so plaster-concrete-concrete-plaster,
          tickness=20+20=40 cm) or will be the drawn wall
          (plaster-concrete, thickness=20cm)?</p>
        <p><br>
        </p>
        <p>THANK YOU</p>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>